Rodney said "It is an indisputable fact that trapped air is a huge problem
in gridded systems and THE reason why pressure relief valves are required on
gridded systems is specifically because of the trapped air in these
systems."

Sorry it's the LACK of trapped air that is the problem as it relates to
pressure.  I suggest you read '02-7.1.2.2 and the handbook.  If you have air
you don't need a pressure relief on a system.  Why?  It's right in the text
of the standard.  Air is compressible.  A spring if you will.  For our
purposes water is not compressible.  With a static system increasing in
temperature the air compresses and stabilizes the pressures.  That's what
the pressure tank on your well is doing, that is what an expansion tank on
an anti-freeze is doing.  Take the air out and there is nothing to compress.
Minor temperature fluctuations then radically change pressure.  I can show
you systems that all the air has been deliberately removed.  It takes a cup
of water to change the pressure a couple psi. 

Ever opened an inspector test valve and waited 30-60 sec for the flow switch
to change position.  That's the trapped air expanding.  Ever opened one and
the flow switch moves immediately that's no air.  For this purpose ignore
the delay watch the lever/paddle position. 

A generalization gridded systems don't have air in them is also false.  It's
exactly related to the location of the ITV.  If the ITV is at the end of the
system on a grid air might be removed while filling or testing.  If the ITV
is at the riser (and there is no air relief remote) there is a similar
amount of air in the system as a tree.  OK all things being equal a gridded
system has less volume compared to a tree system because of pipe size. But
the volume of the system is similar in magnitude.  

I'm with Mark riser ITV with air relief remote and pressure relief someplace
as the best of practice for all systems but I'll add not the minimally
acceptable practice.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rodney Hamm
Sent: Monday, March 09, 2009 5:25 PM
To: [email protected]
Subject: RE: Test/Drain at the Riser

I am writing this response on behalf of any forum members who do not
completely understand some of these issues, not as a direct response to
Mark. The following two paragraphs are from NFPA 13 (2002): 

 

8.16.4.2.1 An alarm test connection not less than 1 in. (25.4 mm) in
diameter, terminating in a smooth bore corrosion-resistant orifice, giving a
flow equivalent to one sprinkler of a type having the smallest orifice
installed on the particular system, shall be provided to test each water
flow alarm device for each system.

 

A.8.16.4.2 This test connection should be in the upper story, and the
connection preferably should be piped from the end of the most remote branch
line. The discharge should be at a point where it can be readily observed.
In locations where it is not practical to terminate the test connection
outside the building, the test connection is permitted to terminate into a
drain capable of accepting full flow under system pressure. In this event,
the test connection should be made using an approved sight test connection
containing a smooth bore corrosion-resistant orifice giving a flow
equivalent to one sprinkler simulating the least flow from an individual
sprinkler in the system.

 

Believe me when I say there are many good reasons for the following text:
"This test connection should be in the upper story, and the connection
preferably should be piped from the end of the most remote branch line." The
fact that so many designers/engineers/installers have decided to simply
ignore this sound advice is perplexing to me.

 

Mark wrote the following: "Placing the ITC at the end of the system will not
guarantee removal of all air from the system. We specify an air bleed valve
be located at the high point(s) of the system for that purpose."  Nobody
said anything about guarantees, I just think we should following good
practices and not be so focused on convenience and/or increasing the profit
associated with the job. What about systems which have sprinkler piping
above fixed ceilings or suspended ceiling tiles? These systems are not very
common now are they (sarcasm)? Most, or nearly all, contractors in my area
do not install "air bleed off valves"; many probably never even considered
the need because they are completely unaware that there is a problem. In
many instances these "air bleed off valves" can be very difficult to access;
why not just follow the GOOD advice outlined in NFPA 13 Section A.8.16.4.2?
Do your customers, the alarm company technicians and the future sprinkler
contractors (the ones who drain the system to add two heads in the new
bathroom) a favor. Provide a suitable ITC and allow everyone who tests or
works on the system to flow water through as much piping as possible and
also through the piping located at the highest portion of the system. 

 

Mark also wrote the following: "The problems associated with air in the
system are valid; that's why a means should be provided to remove the air.
But excessive pressure from temperature rises is not one of those problems.
In fact, it is precisely because of trapped air that most tree systems don't
have excessive pressure problems.  The grids tend to have these issues
because air can't be as readily trapped.  That's why gridded systems should
have a pressure relief. Of course, if you facilitate the removal of most air
from a tree system, then a pressure relief is warranted on that system as
well."  In a more direct response to Mark, I really do not know where to
start. It is an indisputable fact that trapped air is a huge problem in
gridded systems and THE reason why pressure relief valves are required on
gridded systems is specifically because of the trapped air in these systems.
The industry had a significant problem with leaks and accidental system
activation due to air pockets and temperature changes prior to the
requirement of pressure relief valves on these systems; the PRV simply
prevents the system pressure from exceeding 175 psi. The systems were
experiencing system pressures well above 175 psi (sometimes >300 psi)
specifically due to the trapped air and temperature changes caused by
weather fluctuations.

 

In summary, the following is simply my personal opinion: The fact that NFPA
13 allows the ITC to be located at the riser does NOT mean this is a good
idea or a good design.

 

I sincerely thought I was through posting any responses regarding this
subject, but I simply could not refrain in this instance. 

 

Mark, please do not hold any hard feelings towards me, I am simply trying to
help the industry in general and pass on a little of my knowledge through
this forum.

 

Take care,

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

 

Behalf Of Mark Sornsin

Sent: Monday, March 09, 2009 6:44 AM

To: '[email protected]'

Subject: RE: Test/Drain at the Riser

 

Pardon me if this is ground that was already covered-

 

I specify the Inspector's test Connection to be located at the sprinkler

riser. This is NOT something that is new to NFPA-13 either.  E.g., the

1996 edition (4-15.4.2) does not require the location to be at the riser

- it doesn't specify any particular location. Commentary in the handbook

that year specifically states that the purpose of the connection is to

"verify the operation of the water flow alarm device(s)." The appendix

dialogue recommends locating the connection at the remote location of

the system - but this is by no means a requirement.

 

Placing the ITC a the end of the system will not guarantee removal of

all air from the system. We specify an air bleed valve be located at the

high point(s) of the system for that purpose.  I know there are

automatic air releases that can be installed as well.

 

The problems associated with air in the system are valid; that's why a

means should be provided to remove the air.  But excessive pressure from

temperature rises is not one of those problems.  In fact, it is

precisely because of trapped air that that most tree systems don't have

excessive pressure problems.  The grids tend to have these issues

because air can't be as readily trapped.  That's why gridded systems

should have a pressure relief. Of course, if you facilitate the removal

of most air from a tree system, then a pressure relief is warranted on

that system as well.

 

Locating the ITC at the riser will help reduce the amount of new air

into the system, as well as reduce the amount of freshly oxygenated

water as a result of testing.  This will reduce the potential for

additional internal corrosion resulting from the oxygen in the system.

(I seem to recall that this logic is used 'Down Under' as a means to

extend the life of system piping)

 

So, given that the purpose of the ITC on a wet system is to test the

flow alarm, it makes more sense to have it at the riser where it is more

convenient to facilitate the testing. Removal of air should be completed

by air bleed valves or automatic air releases.

 

Mark A. Sornsin, PE

Fire Protection Engineer

Ulteig Engineers, Inc.

3350 38th Avenue S.

Fargo, ND 58104-7079

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to