Hello Chris,

Hmmmmm CPVC in the microwave....    Ha Ha

Wednesday, March 11, 2009, 11:22:41 AM, you wrote:

>SNIP

>                                                Do your same experiment with
> capped steel pipe and see the results through a pressure gauge.  You might
> need the oven or a pot of hot water.  The misses at home or the boss at work
> might get upset if you put steel in the microwave.  The other problem I see
> with your experiment is the scale.  The changes in the water volume may be
> imperceptible to the naked eye.  



> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>  
> 763-658-4483
> 763-658-4921 fax
>  
> Email: [email protected]
>  
> Mail: P.O. Box 69
>         Waverly, MN 55390
>  
> Location: 4439 Hwy 12 SW
>               Waverly, MN 55390
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Rodney Hamm
> Sent: Tuesday, March 10, 2009 8:27 PM
> To: [email protected]
> Subject: Re: Test/Drain at the Riser

> I am sorry to be so blunt, but you need to think a little about what you
> have stated. Air is compressible and water is not compressible. Temperature
> increases or decreases do not affect the pressure of a section of pipe
> filled with 100% water until the water begins to boil. Temperature increases
> will cause the pressure to increase if the same section of pipe is filled
> with air. Temperature decreases will cause the pressure to decrease if the
> same section of pipe is filled with air. 

> If you do not believe me, try a quick little experiment. Take a completely
> 100% full glass of cold water (plastic would be best) pull some saran wrap
> over the top very tight and add a rubber band really tight to make sure no
> air leaks out. Make sure there are no air bubbles on top. Put the full glass
> of water in the microwave on HIGH for 2 minutes. No pressure builds up
> inside the glass because water is not compressible and does not expand.
> Pressure will eventually build if you let the water start to boil. THEN do
> the same exact thing with a glass half full of cold water. Using saran wrap
> and a tight rubber band, you will see the pressure increases dramatically
> and eventually will burst the saran wrap after the balloon effect!

> If you have significant trapped air pockets in a sprinkler system, the ONLY
> time you do not need a PRV is if you are absolutely certain the sprinkler
> piping does not experience significant temperature changes. High temps to
> low temps will cause the pressure to decrease and can potentially allow
> water to enter the system (i.e. false fire alarms) and low temps to high
> temps will cause the pressure to increase and can potentially cause damage
> to the sprinkler system piping (i.e. leaks, ruptures, deformation of
> sprinkler plugs, etc.).

> You stated the following: "With a static system increasing in temperature
> the air compresses and stabilizes the pressures." Actually, in this instance
> increasing the temperature the air does not compress it actually expands and
> instead of stabilizing the static pressure it drastically increases the
> static pressure.

>  

> Rodney K. Hamm, P.E.
> President/Owner
> Falcon Fire Protection
> Office  (478) 953-1677

> Cell  (478) 396-6988

>  

> Date: Tue, 10 Mar 2009 08:53:14 -0500

> From: "Chris Cahill" <[email protected]>

> Subject: RE: Test/Drain at the Riser

> To: <[email protected]>

> Message-ID: <e86bfbe0cd6e4eae97886a3b39d3d...@chris2005>

> Content-Type: text/plain;     charset="us-ascii"

>  

> Rodney said "It is an indisputable fact that trapped air is a huge problem

> in gridded systems and THE reason why pressure relief valves are required on

> gridded systems is specifically because of the trapped air in these

> systems."

>  

> Sorry it's the LACK of trapped air that is the problem as it relates to

> pressure.  I suggest you read '02-7.1.2.2 and the handbook.  If you have air

> you don't need a pressure relief on a system.  Why?  It's right in the text

> of the standard.  Air is compressible.  A spring if you will.  For our

> purposes water is not compressible.  With a static system increasing in

> temperature the air compresses and stabilizes the pressures.  That's what

> the pressure tank on your well is doing, that is what an expansion tank on

> an anti-freeze is doing.  Take the air out and there is nothing to compress.

> Minor temperature fluctuations then radically change pressure.  I can show

> you systems that all the air has been deliberately removed.  It takes a cup

> of water to change the pressure a couple psi. 

>  

> Ever opened an inspector test valve and waited 30-60 sec for the flow switch

> to change position.  That's the trapped air expanding.  Ever opened one and

> the flow switch moves immediately that's no air.  For this purpose ignore

> the delay watch the lever/paddle position. 

>  

> A generalization gridded systems don't have air in them is also false.  It's

> exactly related to the location of the ITV.  If the ITV is at the end of the

> system on a grid air might be removed while filling or testing.  If the ITV

> is at the riser (and there is no air relief remote) there is a similar

> amount of air in the system as a tree.  OK all things being equal a gridded

> system has less volume compared to a tree system because of pipe size. But

> the volume of the system is similar in magnitude.  

>  

> I'm with Mark riser ITV with air relief remote and pressure relief someplace

> as the best of practice for all systems but I'll add not the minimally

> acceptable practice.  

>  

> Chris Cahill, P.E.

> Fire Protection Engineer

> Sentry Fire Protection, Inc.

> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)


-- 
Best regards,
 Charles Thurston                            mailto:[email protected]
  Coastal Fire Protection