With out resorting to the "think" dig I appreciate the conversation and I
think most member do as well.

Compressibility and expansion due to temperature are two entirely different
phenomena.  Compressibility I would describe the volume change as a result
of pushing on something.  Expansion and contraction is the rate of the
molecules trying to get away from each other?  Yes each play on each other
in a closed system with the generic PV=T formula.  Yes that's the IDEAL gas
law and we are far from ideal here.  And the rates of compressibility and
expansion are not the same for the agents here or even related within each
agent.   

I don't know what to say about your experiment other than it's not relevant
to the issue.  With plastic on top you basically have an open system that is
to say the volume of the container can change.  In a steel piping system the
volume of the container can not change.  Or at least to say it changes very
small relative to the size of the system.  Do your same experiment with
capped steel pipe and see the results through a pressure gauge.  You might
need the oven or a pot of hot water.  The misses at home or the boss at work
might get upset if you put steel in the microwave.  The other problem I see
with your experiment is the scale.  The changes in the water volume may be
imperceptible to the naked eye.  

Obviously there is either some disagreement here or at least a communication
issue.  This is good because it will make both of us sharper.      


Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rodney Hamm
Sent: Tuesday, March 10, 2009 8:27 PM
To: [email protected]
Subject: Re: Test/Drain at the Riser

I am sorry to be so blunt, but you need to think a little about what you
have stated. Air is compressible and water is not compressible. Temperature
increases or decreases do not affect the pressure of a section of pipe
filled with 100% water until the water begins to boil. Temperature increases
will cause the pressure to increase if the same section of pipe is filled
with air. Temperature decreases will cause the pressure to decrease if the
same section of pipe is filled with air. 

If you do not believe me, try a quick little experiment. Take a completely
100% full glass of cold water (plastic would be best) pull some saran wrap
over the top very tight and add a rubber band really tight to make sure no
air leaks out. Make sure there are no air bubbles on top. Put the full glass
of water in the microwave on HIGH for 2 minutes. No pressure builds up
inside the glass because water is not compressible and does not expand.
Pressure will eventually build if you let the water start to boil. THEN do
the same exact thing with a glass half full of cold water. Using saran wrap
and a tight rubber band, you will see the pressure increases dramatically
and eventually will burst the saran wrap after the balloon effect!

If you have significant trapped air pockets in a sprinkler system, the ONLY
time you do not need a PRV is if you are absolutely certain the sprinkler
piping does not experience significant temperature changes. High temps to
low temps will cause the pressure to decrease and can potentially allow
water to enter the system (i.e. false fire alarms) and low temps to high
temps will cause the pressure to increase and can potentially cause damage
to the sprinkler system piping (i.e. leaks, ruptures, deformation of
sprinkler plugs, etc.).

You stated the following: "With a static system increasing in temperature
the air compresses and stabilizes the pressures." Actually, in this instance
increasing the temperature the air does not compress it actually expands and
instead of stabilizing the static pressure it drastically increases the
static pressure.

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

Date: Tue, 10 Mar 2009 08:53:14 -0500

From: "Chris Cahill" <[email protected]>

Subject: RE: Test/Drain at the Riser

To: <[email protected]>

Message-ID: <e86bfbe0cd6e4eae97886a3b39d3d...@chris2005>

Content-Type: text/plain;     charset="us-ascii"

 

Rodney said "It is an indisputable fact that trapped air is a huge problem

in gridded systems and THE reason why pressure relief valves are required on

gridded systems is specifically because of the trapped air in these

systems."

 

Sorry it's the LACK of trapped air that is the problem as it relates to

pressure.  I suggest you read '02-7.1.2.2 and the handbook.  If you have air

you don't need a pressure relief on a system.  Why?  It's right in the text

of the standard.  Air is compressible.  A spring if you will.  For our

purposes water is not compressible.  With a static system increasing in

temperature the air compresses and stabilizes the pressures.  That's what

the pressure tank on your well is doing, that is what an expansion tank on

an anti-freeze is doing.  Take the air out and there is nothing to compress.

Minor temperature fluctuations then radically change pressure.  I can show

you systems that all the air has been deliberately removed.  It takes a cup

of water to change the pressure a couple psi. 

 

Ever opened an inspector test valve and waited 30-60 sec for the flow switch

to change position.  That's the trapped air expanding.  Ever opened one and

the flow switch moves immediately that's no air.  For this purpose ignore

the delay watch the lever/paddle position. 

 

A generalization gridded systems don't have air in them is also false.  It's

exactly related to the location of the ITV.  If the ITV is at the end of the

system on a grid air might be removed while filling or testing.  If the ITV

is at the riser (and there is no air relief remote) there is a similar

amount of air in the system as a tree.  OK all things being equal a gridded

system has less volume compared to a tree system because of pipe size. But

the volume of the system is similar in magnitude.  

 

I'm with Mark riser ITV with air relief remote and pressure relief someplace

as the best of practice for all systems but I'll add not the minimally

acceptable practice.  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to