I am fully aware of the "shall" and "should" component. Thanks

 

Steve stated the following: "It's never too late to teach old dogs new
tricks; I think we all have to rid ourselves of the notion that just because
we've been doing something a certain way, that it was necessarily the right
or the best way." I can assure you that I am not against change if change is
warranted, justified or prudent. I believe we should change our approach or
the applicable standards whenever change is warranted or even if there is
simply a better approach. I just do not support changes which have a
detrimental effect and I think we should not allow a change which negatively
impacts the integrity and reliability of the sprinkler systems and/or alarm
systems. We all should do what is best for our customers rather than what
everyone else in the industry is doing. Just because someone convinced the
NFPA committee to allow this approach and "everyone else" in the industry is
placing the ITC at the riser does not mean there are no unintended
consequences. My problem is that so many people in the industry seem
completely unaware of the problems (some even seem like they are avid
proponents of this approach). In this case, I would tend to think just maybe
the "old dogs" placed the ITC at the highest/most remote point of the system
because they were fully aware of the various problems when the ITC was not
at the best location. Back to the "shall" and "should" aspect: I would
venture to say anyone in the industry who consistently ignores the "should"
references throughout the various NFPA documents will undoubtedly find
trouble (The "should" comments might not be required by law, but the
"should" references are typically very good advice). 

 

I certain that I will regret this statement: I am fully aware of the MIC
problem and I agree it is a real problem; however, with regard to this
subject matter, the MIC component is a smoke screen and has been blown way
out off proportion. The impact of MIC is minimal compared to the impact of
an alarm not activating during a true fire emergency or significant water
damage due to a sprinkler system rupture due to excessive system pressures.
Also, systems with very large pockets of trapped air also increase the MIC
problem due to the presence of large volumes of air. I will admit a little
air enters the system each time the ITC is operated due to the new water
molecules and the various air bubbles in the water system; however, this is
a relatively small volume of air compared to systems which have air pockets
as large as 30-70% of the system volume due to the location of the ITC at
the freak'n riser. Wake up people! Why do you think NFPA requires galvanized
sprinkler piping for dry system piping?

 

Oh and I will repeat that I still smile every time I hear or read that "the
sole purpose of the ITC is to test the water flow alarms". So short sighted
and implies a lack of experience/understanding.

 

I sincerely think that I care way too much about this subject and the
sprinkler industry as a whole. I think I am going to focus more time on
coaching my 9 year old's baseball team. Over and out!

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

Date: Mon, 9 Mar 2009 15:38:07 -0700

From: "Steve Leyton" <[email protected]>

Subject: RE: Test/Drain at the Riser

To: <[email protected]>

Message-ID:

      <6d5a59f81dd82b448ceddaf9db6cfeb9788...@server.protectiondesign.local>

Content-Type: text/plain;     charset="us-ascii"

 

Rodney:

 

Welcome to Standards Land, the newest attraction in the non-reality

based theme park called Sprinkler World.

 

Note well that the language you cite conspicuously used the term,

"should", which has been a long-overlooked shortcoming of this

particular section of the standard.    The NFPA manual of style doesn't

provide for the word "should" in the body of the standard - the

"shoulds" SHOULD go in the annex(es).  It has taken the TC this long to

address that sentence in 13.  Also, if you want to discern a technical

committee's "intent", look to the current edition of any standard;

whether or not your state or a local AHJ is using it or not.    If you

look to 8.17.4.2, the language you cite from the 2002 edition has been

revised and the "should" reference completely removed.   If you turn to

the annex - as I did, expecting the "should" to be relocated there - you

will in fact see a comprehensive IMPEACHMENT of the concept that you and

others have implied to be a "good practice".   It's never too late to

teach old dogs new tricks; I think we all have to rid ourselves of the

notion that just because we've been doing something a certain way, that

it was necessarily the right or the best way.

 

Steve Leyton

Protection Design & Consulting

San Diego, CA