Moving to Chat

On Sat, Apr 18, 2009 at 11:57 AM, George Church <[email protected]> wrote:
> A topic change AND a change to CHAT unless we're debating the technical
> merits of 13D/SFD vers the politics of it, which is where we really are,
> which would force us over to CHAT.
>
> Jeez, what a parallel to code interpretations. Tech? Y/N N ->CHAT
> Doggone decision tree.
>
> Steve, I think the above is technical enough to merit staying on the Forum.
>
> glc
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Saturday, April 18, 2009 2:49 PM
> To: [email protected]
> Subject: Re: IMC, IPC and nail plates
>
> And, of course, the other classic example is taking 13D and 13R and
> customizing them with chrome valve covers, lakes pipes, nerf bars,
> moon caps with spinners, etc., (oops, my age is showing--at least I'm
> not talking about jalopies and raccoon tails), trying to turn them
> into property protection systems. I won't even begin to list the
> multitude of local ordinances, amendments and just plain "'cause I
> like its" around here. Couple these unknowables attached, from the
> GC's point of view, to the individual and outrageous water hook-up
> fees and it's no wonder that the builders hate residential sprinklers,
> particularly in small (read sfd) situations where a unknown can mean
> the difference of profit and loss. I'll wager that any one of you out
> there could give a GC a square foot price for a typical sfd that he
> could use and be happy with and I'd bet that if he could rely on that
> rule-of-thumb price to be a percent or two accurate, just like he
> figures glazing, lumber, etc., there'd be almost no opposition to the
> new IRC provisos. A little off topic but I saw an opening and since
> I'm stumping for IRC adoption in Washington I'm going to use every
> venue I can to either convince, cajole or practice what I have to say.
> I'd suggest a topic change if anyone want s to explore this point
> further. Otherwise I'm done for now.
>
> On Sat, Apr 18, 2009 at 10:03 AM, Parsley Consulting
> <[email protected]> wrote:
>> George,
>>
>> Your discussion reminds me very much of a couple of extremely troubling
>> episodes here in California.
>>
>> With the advent of the 2007 edition of NFPA-13 one local jurisdiction
>> adopted it immediately, and had as an effective date 01/01/08.
>> Unfortunately the fire marshal in one district decided that such an
>> adoption meant that project which were not "signed off" and issued a
>> c/o, even if they had been fully permitted and approved under the '02,
>> must now be upgraded to comply with the provisions of the '07 edition.
>> This manifested itself in a "ban" on the use of other than schedule 40
>> or schedule 10 pipe for mains in a sprinkler system as the tables in
>> 9.3.5.3.2 (a) and (b) only covered those types of pipe.  His
>> interpretation was that it was an "implied" requirement from NFPA-13
>> that only those types be allowed for mains. He took the extraordinary
>> (in my view) action of both advising the regional distributor for
>> Dyna-Flow not to ship it to his jurisdiction and refusing to issue a c/o
>> to any project underway unless Dyna-flow mains were removed and replaced
>> with either schedule 40 or schedule 10.  In the face of letters from
>> several individuals from NFPA, AFSA, and OSHPD he was unmoved.
>>
>> Another example of this was a situation that developed here in March.
>> The agency responsible for oversight of construction of public schools
>> here has four separate regional offices, and unfortunately there is a
>> wide range of criteria which are above and beyond those established by
>> NFPA-13, and very little consistency between the offices.  A decision
>> was made at the San Diego office in March which had huge repercussions,
>> in the middle of a project, and quite out of the blue.  When it was
>> learned that the individual making the requirement had the backing of
>> the San Diego office manager, the information was incorporated into an
>> email notice and sent to every local organization of contractors and
>> vendors who might be able to spread the word.  As a courtesy, that
>> message was also sent to the headquarters office of that agency.
>> Twenty-four hours later that policy was rescinded, and another release
>> was emailed out, explaining that the original decision was made without
>> consideration of the parameters of the design criteria for sprinkler
>> systems, and that on this particular topic a strict adherence to NFPA-13
>> requirements was acceptable by this agency.
>>
>> Both are classic examples of the same kind of thinking you're describing
>> with the individual you're dealing with there in PA.  He couldn't find a
>> specific requirement in the applicable documents to support his
>> position, yet was willing to attempt to enforce it because he thought it
>> was a safety issue.
>>
>> Most of the contractors I deal with here and in other parts of the
>> country don't have any real problem following the requirements of the
>> adopted standard, and local or state modifications, provided they are
>> clearly indicated during the bid process.  It is the "out of the blue"
>> criteria which costs us dearly, and delays project completion,
>> particularly in the vise-like economic times we're currently experiencing.
>>
>> Please keep us informed as to how this turns out.
>>
>> PARSLEY CONSULTING
>> Ken Wagoner, SET
>> 760.745.6181 voice
>> 760.745.0537 fax
>> [email protected] <mailto:[email protected]> e-mail
>> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>>
>>
>>
>> George Church wrote:
>>> Rather than agree or disagree, I'll ask you to step away from #13 and
> come
>>> over to #13R, the venue where this is being played out. It's a 3-story
> apt
>>> building under #13R, so #13 only applies as it is brought in by #13R.
>>> Protection of piping from #13 is NOT brought into #13R anywhere (we're in
>>> #13R 2002 edition, BTW) so the #13 requirements for protection of piping
> are
>>> as applicable to a #13R installation as the #13 requirements for
> protecting
>>> an attic- they simply do not apply.
>>>
>>> If there is NO requirement for protecting our piping from mechanical
> injury
>>> (drywall screw) then we're not bound to provide them. Do I think it is
>>> important to protect against them? Yes. Are we taking reasonable steps to
> do
>>> so, at our own option and exceeding the code? Yes. Does this mean I have
> to
>>> invoke how to protect the piping from a non-referenced standard? No.
>>>
>>> If we decided to toss a head at the top of the trash chute on the 4th
> floor
>>> of a #13R hotel, despite the lack of a requirement to provide protection
> in
>>> building service chutes, simply because we want to do so, does this mean
> we
>>> HAVE to install one on the 2nd floor as well, since #13 would have us
> start
>>> at the top and provide them on alternate floors? I don't see how, any
> more
>>> than providing something like this head per #13 at the top level means
> the
>>> corridor protection would have to be delivered at .1 instead of per the
>>> residential head requirements, or providing attic protection above that
> 4th
>>> floor trash chute head.
>>>
>>> Understand the AHJ stated that "even if it isn't in the code, I'm going
> to
>>> require them because I think it is a safety issue". Sorry, the PA UCC
>>> doesn't have a list of safety issues AHJs can enforce and he doesn't have
> a
>>> local amendment either. So I pointed out that as a BCO he can enforce the
>>> adopted law and that is all he can do.
>>>
>>> Naturally this is one of two projects we have in this jurisdiction, the
>>> other is a new FD station. Ironically the chief was arguing with Ken
> about
>>> the need for protection of a walk-in cooler and freezer that are outside
> the
>>> building, but entered at the common wall. We're installing a 2-head AF
> loop
>>> for it, he's arguing no protection is required for a storage area. Holy
> role
>>> reversal!
>>>
>>> It will be interesting to see if I need to drive down for an appeal mtg.
>>>
>>> glc
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Chris
> Cahill
>>> Sent: Friday, April 17, 2009 1:39 PM
>>> To: [email protected]
>>> Subject: RE: IMC, IPC and nail plates
>>>
>>> Well then we agree we disagree, not a problem.  Would be a better world
> if
>>> every agreed with me (mwahahahaha) but it would also be boring, lol.
>>>
>>> Right or wrong I did something similar once as an AHJ and for my life
> can't
>>> recall the specifics. I did win in that in the end the issue was resolved
> my
>>> way.  Never got to a judge I'll admit.  I only lost once as an AHJ on a
>>> standpipe issue and a man of God representing the Cathedral was on the
> other
>>> side of the table.  Up against God I knew I didn't really have a chance.
>>>
>>> My full code path is from the '02 NFPA 13 3.5.5 definition of a riser to
>>> 8.15.4 requirement to protect risers by...other approved means.  No place
> in
>>> 13 describes how to protect so I look in the Code that adopts the
> standard
>>> and find nothing.  Which then invokes 102.7 and off to the IPC/FM/other
> NFPA
>>> documents/listings.
>>>
>>> I believe the reliability of the sprinkler system does fit into the
> overall
>>> scope of the IFC.  But the use of those sections can be more specific.
>  Even
>>> if you don't like the IFC sections the AHJ still has George by the short
>>> hairs with 8.15.4 other approved means.  He's saying the other approved
>>> means is IPC/IMC.  Think the judge is going to overrule.  I don't.
> Certainly
>>> seems reasonable to use another reference on how to that has the exact
> same
>>> purpose - to protect pipe from damage.  It would be up to George to come
> up
>>> with something within our family of codes and standards to refute going
>>> outside.  Sorry George but if it gets to court I don't see you winning.
>  I
>>> promise I'm not for hire to the AHJ or his legal team.
>>>
>>> Don't get me wrong a simple nail plate from the average home improvement
>>> store is sufficient for nearly all applications IMHO.  Going to the
>>> specificity of the IPC/IMC seems a little ridiculous.
>>>
>>> Chris Cahill, P.E.
>>> Fire Protection Engineer
>>> Sentry Fire Protection, Inc.
>>>
>>> 763-658-4483
>>> 763-658-4921 fax
>>>
>>> Email: [email protected]
>>>
>>> Mail: P.O. Box 69
>>>         Waverly, MN 55390
>>>
>>> Location: 4439 Hwy 12 SW
>>>               Waverly, MN 55390
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Jeff
> Hewitt
>>> Sent: Friday, April 17, 2009 11:59 AM
>>> To: [email protected]
>>> Subject: RE: IMC, IPC and nail plates
>>>
>>> Chris,
>>>
>>> I respectfully disagree,
>>>
>>> IFC 2006 102.7 and 102.8 can only be applied within the overall SCOPE of
> the
>>> entire IFC document which is limited to Fire Suppression conditions, not
>>> Mechanical, and not Plumbing.  The Scope is found in IFC 2006 101.2
>>>
>>> Also, according to IFC 2006 102.6 Referenced Codes and Standards,
>>>
>>>       "the codes and standards referenced in this code shall be those
> that
>>> are listed in Chapter 45 and such codes and standards shall   be
>>> considered part of the requirements of this code to the prescribed extent
> of
>>> each such reference."
>>>
>>> The commentary to IFC 2206 102.6 states:
>>>
>>>       "the application of referenced standards is limited to those
>>> portions of the standards that are specifically identified."
>>>
>>> Please note that in IFC 2006 Chapter 45, where the reference standards
> and
>>> codes are listed, IPC 2006 305.8, and IMC 2006 305.5 are NOT specifically
>>> listed/referenced.
>>>
>>>
>>> Jeff Hewitt, PE, SET, SFPE (Professional Member)
>>> Corporate Engineer
>>> Bi-State Fire Protection Corporation
>>> 241 Hughes Lane
>>> St. Charles, MO  63301
>>>
>>> 636-946-0011
>>> 636-946-5172 (fax)
>>> 314-574-6989 (cell)
>>>
>>> Fire Sprinklers Save lives.
>>> Can You Live Without Them?
>>>
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Chris
> Cahill
>>> Sent: Friday, April 17, 2009 10:53 AM
>>> To: [email protected]
>>> Subject: RE: IMC, IPC and nail plates
>>>
>>> Does our family of codes go into this level of detail?  If not and I
> don't
>>> think it does, the authority for the AHJ to use what Thom quoted is IFC
>>> 102.7 or IFC 102.8.
>>>
>>> Chris Cahill, P.E.
>>> Fire Protection Engineer
>>> Sentry Fire Protection, Inc.
>>>
>>> 763-658-4483
>>> 763-658-4921 fax
>>>
>>> Email: [email protected]
>>>
>>> Mail: P.O. Box 69
>>>         Waverly, MN 55390
>>>
>>> Location: 4439 Hwy 12 SW
>>>               Waverly, MN 55390
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Jeff
> Hewitt
>>> Sent: Friday, April 17, 2009 10:40 AM
>>> To: [email protected]
>>> Subject: RE: IMC, IPC and nail plates
>>>
>>> I think you are missing the point.
>>>
>>> You have found the references within each Code, but do the Codes apply to
>>> Fire Suppression piping?
>>>
>>> Read the SCOPE of each document and you will find that it does NOT
> include
>>> Fire Suppression piping.
>>>
>>> Jeff Hewitt, PE, SET, SFPE (Professional Member)
>>> Corporate Engineer
>>> Bi-State Fire Protection Corporation
>>> 241 Hughes Lane
>>> St. Charles, MO  63301
>>>
>>> 636-946-0011
>>> 636-946-5172 (fax)
>>> 314-574-6989 (cell)
>>>
>>> Fire Sprinklers Save lives.
>>> Can You Live Without Them?
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Thom
> McMahon
>>> Sent: Friday, April 17, 2009 10:28 AM
>>> To: [email protected]
>>> Subject: RE: IMC, IPC and nail plates
>>>
>>>
>>> IPC 2006
>>> 305.8 Protection against physical damage. In concealed
>>> locations where piping, other than cast-iron or galvanized steel,
>>> is installed through holes or notches in studs, joists, rafters or
>>> similar members less than 1.5 inches (38 mm) from the nearest
>>> edge of the member, the pipe shall be protected by shield plates.
>>> Protective shield plates shall be a minimum of
>>> 0.062-inch-thick (1.6 mm) steel, shall cover the area of the pipe
>>> where the member is notched or bored, and shall extend a minimum
>>> of 2 inches (51 mm) above sole plates and below top
>>> plates.
>>>
>>> IMC 2006
>>> 305.5 Protection against physical damage. In concealed
>>> locations where piping, other than cast-iron or steel, is installed
>>> through holes or notches in studs, joists, rafters or similar members
>>> less than 1.5 inches (38 mm) from the nearest edge of the
>>> member, the pipe shall be protected by shield plates. Protective
>>> shield plates shall be a minimum of 0.062-inch-thick (1.6 mm)
>>> steel, shall cover the area of the pipe where the member is
>>> notched or bored, and shall extend a minimum of 2 inches (51 mm) above
>>> sole plates and below top plates.
>>>
>>> Here's how we deal with this.
>>> We nail plate the sole plates(one or up to 3 depending on the
> construction,
>>> houses with gypcrete floors typically have an extra plate or two
> depending
>>> upon how thick the gyp is.) and slip a steel sleeve around the riser
> coming
>>> thru the plate.(We find we have enough scrap pipe around to keep a
> constant
>>> supply of 8" sleeves. We use 8" because we have base moldings here that
> go
>>> to 10" high on occasion.)
>>>
>>> Most walls we see are double plates at the top. Only the upper plate is
> the
>>> actual "Top Plate" the second plate has a name I forget right now. Any
> way
>>> we nail plate both plates and have our "Nominal" 2" below the top plate.
>>> We've never had any problem with doing this from any inspector.
>>>
>>>
>>> Thom McMahon, SET
>>> Firetech, Inc.
>>> 2560 Copper Ridge Dr
>>> P.O. Box 882136
>>> Steamboat Springs, CO 80488
>>> Tel:  970-879-7952
>>> Fax: 970-879-7926
>>>
>>>
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of George
> Church
>>> Sent: Friday, April 17, 2009 7:59 AM
>>> To: [email protected]
>>> Subject: IMC, IPC and nail plates
>>>
>>> Had an interesting encounter with an AHJ this week.
>>> He stopped by a jobsite where we're installing CPVC in walls, and found
>>> fault with the nail plates we're using.
>>> I called to follow up on why he didn't like them, and asked for a code
>>> reference. He replied even if it wasn't in the code, he'd enforce
> nailplates
>>> extending further than ours as a safety issue. So I reminded him that his
>>> authority was to enforce the PA UCC as adopted, not safety issues he took
> a
>>> personal liking to.
>>>
>>> His code reference arrived by USPS this AM. He cited the IPC and IMC as
>>> applicable to sprinkler piping, which I disagree with.
>>>
>>> Any thoughts or previous rulings by other AHJs?
>>>
>>> George Church
>>> Rowe Sprinkler
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>>
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....