Thom,

All well and good but if you recall George's original post it wasn't
with protecting or not protecting the piping but that the AHJ had
conjured a specific method (16 gauge plates I believe) from an outside
code not referenced from IBC chapter 9, the chapter which specifically
references NFPA 13R (in this case) as the appropriate document and
which doesn't reference the documents the AHJ is hanging his hat on.
George's argument is that since NFPA 13R does not require a specific
metal gauge for protection at all (your references aside which still
say nothing regarding specific gauges of metal) that citing specific
requirements from non-referenced documents is inappropriate. Whether
or not 13R is lacking in this regard is irrelevant and shifts us over
to that what ought or ought not to be political stuff.

On Sun, Apr 19, 2009 at 10:18 AM, Thom McMahon <[email protected]> wrote:
> Relying solely on 13R may give you righteous reason for outrage at the
> official, but you may want to look carefully at 6.1.4.4 protection of
> risers, if it is risers he is asking you to protect. And also look at
> 6.2.7(17) submission requirements for "Protection of nonmetallic pipe".
>
> An just as a final aside, IBC/IMC/IPC/IEC all require additional protection
> of all system components when there is less than an 11/2" of wood from the
> face of the stud to the hole, pipe, wire or service.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to