I'm still waiting on the model that will give a hint that the latest  
work on an area left a valve closed so the calculated loop is invalid.

Roland

On May 12, 2009, at 11:05 AM, R Richardson wrote:

> Hi Thom,
>
> Thanks for the feedback.  We have been operating under the same set  
> of assumptions you are speaking of and we are starting to see lots  
> of issues about old pipe becoming severely tuberculated (for example  
> the water map shows a 8 in main, but the water test shows the main  
> to now be equivalent to a 4 in main.  Some of the older pipe that  
> was installed is unlined DI, the tuberculation is brutal.  The  
> concrete lined DI does not share the same problem
>
> So, be careful about assuming the pipe is good, if it was unlined it  
> may be much smaller than what it was originally.
>
> Rich

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to