Ok. I'm falling off the fence and back to my original side. This is
where this whole interchange shines. I always rely on you guys to have
those thoughts that I miss.

On Sun, May 17, 2009 at 8:31 PM, Ron Greenman <[email protected]> wrote:
> The red faced one. I do though think all the commentary has applied
> across all the flavors of 13.
>
> On Sun, May 17, 2009 at 6:47 PM, Thomas Watt <[email protected]> wrote:
>>  What colored bear said this was a 13D system?    :)
>>
>> Go Magic!!!
>>
>>
>>
>> ----- Original Message -----
>> From: "Ron Greenman" <[email protected]>
>> To: <[email protected]>
>> Sent: Sunday, May 17, 2009 6:35 PM
>> Subject: Re: CPVC w/o water between riser and FDC
>>
>>
>> That was 2007 but it's in 2002 also and also in 4.3.2. Also, in A.4.3
>> there are recommendations on hydro testing DRY systems. Remember that
>> dry systems are not prohibited by 13D. They are just not acceptable at
>> the moment due to listing restrictions. And now I'm considering
>> reversing my opinion. Since BlazemMaster specifically states it is NOT
>> to be used in dry systems does that also mean the dry section of FDCs?
>> BlazeMaster is silent on the subject so must you take the dry system
>> prohibition and apply it to any dry part of a BlazeMaster
>> installation? The silence seems to suggest just that. I haven't
>> completely changed camps so quickly but I'm sitting on the fence. I
>> love public discussion. It allows you to think out loud and show the
>> entire world how big a fool you can be. I have a photo (Photoshopped
>> for sure) of a fox's head amid a sea of beagles. The caption reads,
>> "When you are in deep trouble, say nothing and try to look
>> inconspicuous." I think I'll take my own advice.
>>
>> On Sun, May 17, 2009 at 2:50 PM, Thomas Watt <[email protected]> wrote:
>>> assume, practical...are those definitions in the 2007 edition? I can't
>>> find
>>> them in 2002.
>>>
>>> I included the reference only to show the importance the manufacturer
>>> places
>>> on removal of air from the system. I assume it is not only the water
>>> hammer
>>> issue but the real possibility of distortion or failure(burn-through).
>>> (A.6.3.6 NFPA 13 2002 ed.)
>>>
>>> I have found nothing quite as disconcerting as walking through a jobsite
>>> on
>>> a monday morning to find heads, escutcheons and burned off head adaptors
>>> littering the floor.
>>> Lightning struck roof, system 2 weeks from hydro.
>>>
>>> ----- Original Message -----
>>> From: "Ron Greenman" <[email protected]>
>>> To: <[email protected]>
>>> Sent: Saturday, May 16, 2009 8:26 PM
>>> Subject: Re: CPVC w/o water between riser and FDC
>>>
>>>
>>> Thomas,
>>>
>>> When applying water to the FDC we can assume we are doing so to a pipe
>>> that has already been tested for integrity and not worrying about dry
>>> fits, unconnected pieces, etc. as we would in a new system (property
>>> damage), nor full of air as we experience in a new system (potential
>>> explosive decompression and the resultant bodily injury). We can also
>>> assume that we are adding water to supplement a flow that is already
>>> occurring and therefore there are "holes" (discharging heads) already
>>> in the pipe. Unless we unleash the damned hellish hounds of hundreds
>>> of pounds of over-pressurization upon the system I doubt that we will
>>> even have the mildest of water hammer. And as a side note we have
>>> hooked this FDC up to the truck because the building is on fire and
>>> already experiencing property damage. Now should the pipe run from the
>>> FDC be as short as possible? Certainly the dry portion, and we can
>>> limit an FDC dry run of 100 feet (or more, or less) by placing the FDC
>>> check valve as close as practical to the FDC itself. But if placing it
>>> at the riser is the most practical location (my ridiculous 100 foot
>>> run excepted) then so be it. I wonder how much pressure I would have
>>> to apply to a CPVC system with only one head flowing before I've
>>> created a situation that would rupture piping and connections already
>>> tested to 200 psi in a static state? I'd bet more than my fire engine
>>> could generate.
>>>
>>> On Sat, May 16, 2009 at 4:38 PM, Thomas Watt <[email protected]> wrote:
>>>> IMHO, no.
>>>>
>>>> The FDC check should be installed as close as possible to the FDC to
>>>> eliminate the dry run.
>>>>
>>>> >From the Harvel install guide:
>>>> "When pressure testing, the sprinkler system shall be slowly filled
>>>>
>>>> with water and the air bled from the highest and farthest sprinkler
>>>>
>>>> heads before pressure testing is applied. Air must be removed from
>>>>
>>>> piping systems (plastic or metal) to prevent it from being locked in
>>>>
>>>> the system when pressure is applied. Entrapped air can generate
>>>>
>>>> excessive surge pressures that can result in bodily injury and/or
>>>>
>>>> property damage, regardless of the piping materials used."
>>>>
>>>>
>>>>
>>>> ----- Original Message -----
>>>> From: "R Richardson" <[email protected]>
>>>> To: <[email protected]>
>>>> Sent: Friday, May 15, 2009 1:04 PM
>>>> Subject: CPVC w/o water between riser and FDC
>>>>
>>>>
>>>>> We are reviewing a proposal for a wet pipe sprinkler system using CPVC
>>>>> pipe. However, there is a run of CPVC pipe between the FDC and the riser
>>>>> that is dry, is this standard practice or acceptable?
>>>>>
>>>>> Thanks,
>>>>>
>>>>> Rich Richardson
>>>>> Seattle Fire Department
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>> For Technical Assistance, send an email to:
>>>>> [email protected]
>>>>>
>>>>> To Unsubscribe, send an email
>>>>> to:[email protected]
>>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>>
>>>> --------------------------------------------------------------------------------
>>>>
>>>>
>>>>
>>>> Internal Virus Database is out of date.
>>>> Checked by AVG - http://www.avg.com
>>>> Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date:
>>>> 2/2/2009
>>>> 7:51 AM
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>
>>>
>>>
>>> --
>>> Ron Greenman
>>> at home....
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>>
>>> --------------------------------------------------------------------------------
>>>
>>>
>>>
>>> Internal Virus Database is out of date.
>>> Checked by AVG - http://www.avg.com
>>> Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date: 2/2/2009
>>> 7:51 AM
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>>
>> --
>> Ron Greenman
>> at home....
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>>
>> --------------------------------------------------------------------------------
>>
>>
>>
>> Internal Virus Database is out of date.
>> Checked by AVG - http://www.avg.com
>> Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date: 2/2/2009
>> 7:51 AM
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> at home....
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to