The red faced one. I do though think all the commentary has applied
across all the flavors of 13.

On Sun, May 17, 2009 at 6:47 PM, Thomas Watt <[email protected]> wrote:
>  What colored bear said this was a 13D system?    :)
>
> Go Magic!!!
>
>
>
> ----- Original Message -----
> From: "Ron Greenman" <[email protected]>
> To: <[email protected]>
> Sent: Sunday, May 17, 2009 6:35 PM
> Subject: Re: CPVC w/o water between riser and FDC
>
>
> That was 2007 but it's in 2002 also and also in 4.3.2. Also, in A.4.3
> there are recommendations on hydro testing DRY systems. Remember that
> dry systems are not prohibited by 13D. They are just not acceptable at
> the moment due to listing restrictions. And now I'm considering
> reversing my opinion. Since BlazemMaster specifically states it is NOT
> to be used in dry systems does that also mean the dry section of FDCs?
> BlazeMaster is silent on the subject so must you take the dry system
> prohibition and apply it to any dry part of a BlazeMaster
> installation? The silence seems to suggest just that. I haven't
> completely changed camps so quickly but I'm sitting on the fence. I
> love public discussion. It allows you to think out loud and show the
> entire world how big a fool you can be. I have a photo (Photoshopped
> for sure) of a fox's head amid a sea of beagles. The caption reads,
> "When you are in deep trouble, say nothing and try to look
> inconspicuous." I think I'll take my own advice.
>
> On Sun, May 17, 2009 at 2:50 PM, Thomas Watt <[email protected]> wrote:
>> assume, practical...are those definitions in the 2007 edition? I can't
>> find
>> them in 2002.
>>
>> I included the reference only to show the importance the manufacturer
>> places
>> on removal of air from the system. I assume it is not only the water
>> hammer
>> issue but the real possibility of distortion or failure(burn-through).
>> (A.6.3.6 NFPA 13 2002 ed.)
>>
>> I have found nothing quite as disconcerting as walking through a jobsite
>> on
>> a monday morning to find heads, escutcheons and burned off head adaptors
>> littering the floor.
>> Lightning struck roof, system 2 weeks from hydro.
>>
>> ----- Original Message -----
>> From: "Ron Greenman" <[email protected]>
>> To: <[email protected]>
>> Sent: Saturday, May 16, 2009 8:26 PM
>> Subject: Re: CPVC w/o water between riser and FDC
>>
>>
>> Thomas,
>>
>> When applying water to the FDC we can assume we are doing so to a pipe
>> that has already been tested for integrity and not worrying about dry
>> fits, unconnected pieces, etc. as we would in a new system (property
>> damage), nor full of air as we experience in a new system (potential
>> explosive decompression and the resultant bodily injury). We can also
>> assume that we are adding water to supplement a flow that is already
>> occurring and therefore there are "holes" (discharging heads) already
>> in the pipe. Unless we unleash the damned hellish hounds of hundreds
>> of pounds of over-pressurization upon the system I doubt that we will
>> even have the mildest of water hammer. And as a side note we have
>> hooked this FDC up to the truck because the building is on fire and
>> already experiencing property damage. Now should the pipe run from the
>> FDC be as short as possible? Certainly the dry portion, and we can
>> limit an FDC dry run of 100 feet (or more, or less) by placing the FDC
>> check valve as close as practical to the FDC itself. But if placing it
>> at the riser is the most practical location (my ridiculous 100 foot
>> run excepted) then so be it. I wonder how much pressure I would have
>> to apply to a CPVC system with only one head flowing before I've
>> created a situation that would rupture piping and connections already
>> tested to 200 psi in a static state? I'd bet more than my fire engine
>> could generate.
>>
>> On Sat, May 16, 2009 at 4:38 PM, Thomas Watt <[email protected]> wrote:
>>> IMHO, no.
>>>
>>> The FDC check should be installed as close as possible to the FDC to
>>> eliminate the dry run.
>>>
>>> >From the Harvel install guide:
>>> "When pressure testing, the sprinkler system shall be slowly filled
>>>
>>> with water and the air bled from the highest and farthest sprinkler
>>>
>>> heads before pressure testing is applied. Air must be removed from
>>>
>>> piping systems (plastic or metal) to prevent it from being locked in
>>>
>>> the system when pressure is applied. Entrapped air can generate
>>>
>>> excessive surge pressures that can result in bodily injury and/or
>>>
>>> property damage, regardless of the piping materials used."
>>>
>>>
>>>
>>> ----- Original Message -----
>>> From: "R Richardson" <[email protected]>
>>> To: <[email protected]>
>>> Sent: Friday, May 15, 2009 1:04 PM
>>> Subject: CPVC w/o water between riser and FDC
>>>
>>>
>>>> We are reviewing a proposal for a wet pipe sprinkler system using CPVC
>>>> pipe. However, there is a run of CPVC pipe between the FDC and the riser
>>>> that is dry, is this standard practice or acceptable?
>>>>
>>>> Thanks,
>>>>
>>>> Rich Richardson
>>>> Seattle Fire Department
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> For Technical Assistance, send an email to:
>>>> [email protected]
>>>>
>>>> To Unsubscribe, send an email
>>>> to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>
>>>
>>> --------------------------------------------------------------------------------
>>>
>>>
>>>
>>> Internal Virus Database is out of date.
>>> Checked by AVG - http://www.avg.com
>>> Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date:
>>> 2/2/2009
>>> 7:51 AM
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>>
>> --
>> Ron Greenman
>> at home....
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>>
>> --------------------------------------------------------------------------------
>>
>>
>>
>> Internal Virus Database is out of date.
>> Checked by AVG - http://www.avg.com
>> Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date: 2/2/2009
>> 7:51 AM
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> --------------------------------------------------------------------------------
>
>
>
> Internal Virus Database is out of date.
> Checked by AVG - http://www.avg.com
> Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date: 2/2/2009
> 7:51 AM
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to