Thomas,

When applying water to the FDC we can assume we are doing so to a pipe
that has already been tested for integrity and not worrying about dry
fits, unconnected pieces, etc. as we would in a new system (property
damage), nor full of air as we experience in a new system (potential
explosive decompression and the resultant bodily injury).  We can also
assume that we are adding water to supplement a flow that is already
occurring and therefore there are "holes" (discharging heads) already
in the pipe. Unless we unleash the damned hellish hounds of hundreds
of pounds of over-pressurization upon the system I doubt that we will
even have the mildest of water hammer. And as a side note we have
hooked this FDC up to the truck because the building is on fire and
already experiencing property damage. Now should the pipe run from the
FDC be as short as possible? Certainly the dry portion, and we can
limit an FDC dry run of 100 feet (or more, or less) by placing the FDC
check valve as close as practical to the FDC itself. But if placing it
at the riser is the most practical location (my ridiculous 100 foot
run excepted) then so be it. I wonder how much pressure I would have
to apply to a CPVC system with only one head flowing before I've
created a situation that would rupture piping and connections already
tested to 200 psi in a static state? I'd bet more than my fire engine
could generate.

On Sat, May 16, 2009 at 4:38 PM, Thomas Watt <[email protected]> wrote:
> IMHO, no.
>
> The FDC check should be installed as close as possible to the FDC to
> eliminate the dry run.
>
> >From the Harvel install guide:
> "When pressure testing, the sprinkler system shall be slowly filled
>
> with water and the air bled from the highest and farthest sprinkler
>
> heads before pressure testing is applied. Air must be removed from
>
> piping systems (plastic or metal) to prevent it from being locked in
>
> the system when pressure is applied. Entrapped air can generate
>
> excessive surge pressures that can result in bodily injury and/or
>
> property damage, regardless of the piping materials used."
>
>
>
> ----- Original Message -----
> From: "R Richardson" <[email protected]>
> To: <[email protected]>
> Sent: Friday, May 15, 2009 1:04 PM
> Subject: CPVC w/o water between riser and FDC
>
>
>> We are reviewing a proposal for a wet pipe sprinkler system using CPVC
>> pipe.  However, there is a run of CPVC pipe between the FDC and the riser
>> that is dry, is this standard practice or acceptable?
>>
>> Thanks,
>>
>> Rich Richardson
>> Seattle Fire Department
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
>
> --------------------------------------------------------------------------------
>
>
>
> Internal Virus Database is out of date.
> Checked by AVG - http://www.avg.com
> Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date: 2/2/2009
> 7:51 AM
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to