Rich,

The pipe is good for working 175 psi and is hydroed like any other
pipe. It's not the dry that's a problem but the dry pipe system that
it's not listed for.

On Fri, May 15, 2009 at 10:07 AM, Steve Leyton
<[email protected]> wrote:
> We have never been concerned with this and I'd say it's standard
> practice on most 13R systems throughout the Southwest.   It's generally
> a short run of pipe if the FDC is on the wall.
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of R
> Richardson
> Sent: Friday, May 15, 2009 10:04 AM
> To: [email protected]
> Subject: CPVC w/o water between riser and FDC
>
> We are reviewing a proposal for a wet pipe sprinkler system using CPVC
> pipe.  However, there is a run of CPVC pipe between the FDC and the
> riser that is dry, is this standard practice or acceptable?
>
> Thanks,
>
> Rich Richardson
> Seattle Fire Department
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4080 (20090515) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4080 (20090515) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to