Tom,

I'm in a good mood today, decent weather has finally come to a weekend
in the North Wet so I'm feeling a bit devilish and I intend to have a
bit of fun at your expense. If you look at the BlazeMaster install
manual it allows exposed CPVC in certain occupancies including
residential, but all exposed piping must be protected by the system.
The piping, except risers, must be on the ceiling if a ceiling system
and on the wall near the ceiling if a sidewall system. Smooth flat
ceiling in both cases. And since a lot of time is spent talking about
the system and the riser regarding exposed piping, but nothing about
the FDC, in all (13D/13R/13) systems I'd venture an interpretation
that the FDC is not allowed to be exposed whether protected or not
simply by the silence of the manual. 13D/2007 4.3.2 says you SHALL
hydrotest per NFPA 13 when an FDC is present. Older editions also
state the same though in different sections. Now if doing all this
non-CPVC work is your choice then who cares except you and your
client. Of course not doing the hydro is beyond just "your bad" and
someone(s) is screwing the pooch on that one. My real concern with
your comments is that some AHJ might get the idea that your method is
better, and there's nothing but opinion, as you said, behind it, and
will decide that all FDCs need to meet your personal
standards/requirements because they're "better." Remember that this
thread started with the Chief Engineer from Seattle Fire asking the
question. I know Rich and can guess what he's fishing for when asking
for opinion on this Forum. I know that if he chooses to disallow
plastic FDCs it will be because he's thoughtfully weighed all the
opinions presented here, information he's gleaned from other sources
and opinions from the other engineering types at SFD and, if all FDCs
in Seattle need to be metal, then so be it. It is a decision made
thoughtfully. The guys that scare me are the AHJs that decide they
want plumbing fixture flows added to calcs on big SFDs (those ones
with six bathrooms, two laundry rooms, a main kitchen and a second
kitchen near the BBQ deck) not because the family that lives there
uses that much more water but because those people "have a lot of
parties (toilet flushing parties I call them) and use a lot of water
and there might be a fire." My answer to that is then don't modify 13D
for some property protection issue (can we assume that people at a
party that are using water are awake and ambulatory and able to leave
the building quickly for life safety purposes?). If property
protection is a concern then require (obviously the owners are not
getting good consultation from the A/Es or the GC if they're only
installing 13D for their seven figure homes) a full 13 system on these
behemoths. How many jurisdictions require costly add-ons (garage
protection (I know of one jurisdiction that argues that they require
garages to be sprinklered because MANY home owners in the jurisdiction
also use their garages to park their seaplanes in--I don't know about
you but I keep my seaplane--oh wait, I don't have one nor know anyone
that does), closets, small bathrooms, attics, etc.) that the NAHB/BIA
then use as rationale for why sprinklers are too expensive in houses?
Unfortunately 13D Scope & Purpose both mention property protection and
so there's a peg to hang these expensive amendments on. Off the soap
box now. And I think I'll become a Bostonian for this season so Go Red
Sox.

On Sun, May 17, 2009 at 7:02 AM, Tom Duross <[email protected]> wrote:
> I dunno.  I'd have a hard time walking away from a cpvc FDC line empty and
> subject to melting or burning.  I've done a fair amount of 13D/R and SFD's
> and I've never used cpvc for any controls work or drains.  I suppose if the
> line was protected in most fashions I'd be a little more at ease about using
> it but I'd feel a lot better using steel or copper.  I rarely pressure test
> the FDC line on a SFD if I even have one which is rare but we use brazed L
> copper on 9 out of 10 D and R systems anyway from the service connection to
> the riser manifold, and threaded galvy for anything like FDC's or drains
> (normally dry sections).  MY bad I know but a judgment call I made long ago
> and stay with it.  I've weighed the material costs and it's really not that
> much more, labor's another story.  I can see how it's quicker, cheaper and
> easier and I've seen my share of others doing this and more.  I don't mean
> to say it's wrong or anything wrong with it if it meets code and is
> approved, just not for me.  I usually hook most projects into the first year
> of ITM as part of the design and installation and try my hardest to keep
> them year after year so all the more reason I don't want any potential
> issues and also can't blame the installer in case anything goes wrong.  :P
> Just my opinion.  I am pleased to boast my ITM income surpassed my
> construction income on 2008 and I couldn't be happier, except for the
> increased insurance costs.
>
> Tom Duross
> Let's Go Red Sox!
>
>
>
> Thomas,
>
> When applying water to the FDC we can assume we are doing so to a pipe
> that has already been tested for integrity and not worrying about dry
> fits, unconnected pieces, etc. as we would in a new system (property
> damage), nor full of air as we experience in a new system (potential
> explosive decompression and the resultant bodily injury).  We can also
> assume that we are adding water to supplement a flow that is already
> occurring and therefore there are "holes" (discharging heads) already
> in the pipe. Unless we unleash the damned hellish hounds of hundreds
> of pounds of over-pressurization upon the system I doubt that we will
> even have the mildest of water hammer. And as a side note we have
> hooked this FDC up to the truck because the building is on fire and
> already experiencing property damage. Now should the pipe run from the
> FDC be as short as possible? Certainly the dry portion, and we can
> limit an FDC dry run of 100 feet (or more, or less) by placing the FDC
> check valve as close as practical to the FDC itself. But if placing it
> at the riser is the most practical location (my ridiculous 100 foot
> run excepted) then so be it. I wonder how much pressure I would have
> to apply to a CPVC system with only one head flowing before I've
> created a situation that would rupture piping and connections already
> tested to 200 psi in a static state? I'd bet more than my fire engine
> could generate.
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....