IMHO, no.

The FDC check should be installed as close as possible to the FDC to 
eliminate the dry run.

>From the Harvel install guide:
"When pressure testing, the sprinkler system shall be slowly filled

with water and the air bled from the highest and farthest sprinkler

heads before pressure testing is applied. Air must be removed from

piping systems (plastic or metal) to prevent it from being locked in

the system when pressure is applied. Entrapped air can generate

excessive surge pressures that can result in bodily injury and/or

property damage, regardless of the piping materials used."



----- Original Message ----- 
From: "R Richardson" <[email protected]>
To: <[email protected]>
Sent: Friday, May 15, 2009 1:04 PM
Subject: CPVC w/o water between riser and FDC


> We are reviewing a proposal for a wet pipe sprinkler system using CPVC 
> pipe.  However, there is a run of CPVC pipe between the FDC and the riser 
> that is dry, is this standard practice or acceptable?
>
> Thanks,
>
> Rich Richardson
> Seattle Fire Department
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)


--------------------------------------------------------------------------------



Internal Virus Database is out of date.
Checked by AVG - http://www.avg.com
Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date: 2/2/2009 
7:51 AM

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to