NFPA 13, 2007
A.22.4.4.8 The use of sprinklers with differing orifice sizes in
situations where different protection areas are needed is not considered
balancing. An example would be a room that could be
protected with sprinklers having different orifice size in closet,
foyer, and room areas. However, this procedure introduces difficulties
when restoring a system to service after operation since it
is not always clear which sprinklers go where.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Randy Knutson
Sent: Monday, June 15, 2009 11:42 AM
To: [email protected]
Subject: Mixing k-factors in paintspray booths

Forum Members,

 

Can I use a smaller k-factor sprinkler in the pit and exhaust plenum of a
paint spray booth?

Due to the geometry of the pit and exhaust plenum. The sprinklers in there
are covering about 36 square feet per sprinkler.

Any insight would be appreciated.

 

Randy Knutson

Shilo Automatic Sprinkler, Inc.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to