Here's a little more info for you guys and thanks again for the help. I'm using 
8.0k above and 5.6k in the pit and plenum. The booth is going in 500 ft away 
from the riser and there are 15 sprinklers in this booth 8 above and
7 in the pit and plenum. I'm trying to cut on down on the bulk main supplying 
the booth.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Randy Knutson
Sent: Monday, June 15, 2009 12:06 PM
To: [email protected]
Subject: RE: Mixing k-factors in paintspray booths

Thanks Thom.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Monday, June 15, 2009 11:56 AM
To: [email protected]
Subject: RE: Mixing k-factors in paintspray booths

NFPA 13, 2007
A.22.4.4.8 The use of sprinklers with differing orifice sizes in situations 
where different protection areas are needed is not considered balancing. An 
example would be a room that could be protected with sprinklers having 
different orifice size in closet, foyer, and room areas. However, this 
procedure introduces difficulties when restoring a system to service after 
operation since it is not always clear which sprinklers go where.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Randy Knutson
Sent: Monday, June 15, 2009 11:42 AM
To: [email protected]
Subject: Mixing k-factors in paintspray booths

Forum Members,

 

Can I use a smaller k-factor sprinkler in the pit and exhaust plenum of a paint 
spray booth?

Due to the geometry of the pit and exhaust plenum. The sprinklers in there are 
covering about 36 square feet per sprinkler.

Any insight would be appreciated.

 

Randy Knutson

Shilo Automatic Sprinkler, Inc.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to