If you're trying to save a few gpm by going with the smaller orifice, it's 
really not worth the effort.  Plus unless you're bagging the heads, smaller 
orifice is more likely to get clogged sooner than larger orifice from the 
spraying effort.  In addition, depending on the hazard you're protecting, a 
little cushion on the discharge side may not be a bad thing.  No need to shave 
the hydraulics that close.  When heads get covered and need to be replaced, the 
smaller orifice probably won't be noticed and the head will be replaced with a 
standard 5.6 anyway.  Keep it simple.   

What is the key material being sprayed?


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Randy Knutson
Sent: Monday, June 15, 2009 1:42 PM
To: [email protected]
Subject: Mixing k-factors in paintspray booths

Forum Members,

 

Can I use a smaller k-factor sprinkler in the pit and exhaust plenum of a paint 
spray booth?

Due to the geometry of the pit and exhaust plenum. The sprinklers in there are 
covering about 36 square feet per sprinkler.

Any insight would be appreciated.

 

Randy Knutson

Shilo Automatic Sprinkler, Inc.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to