I beg to differ my friend.  SOMETIMES it's not worth the effort but
SOMETIMES it is.  Perhaps it's no big deal in a large industrial site with
multiple fire pumps.  Which I think is your typical business.  When dealing
with 50 psi statics shaving a few gpm here and there saves a lot of fire
pumps where they are otherwise not needed.  OK maybe not a lot but certainly
some.  That's some big $$$$ saving with the difference of not throwing away
water using smaller k's.  Then there is main size saving potentially.  A
little balancing as allowed can cut 100 gpm off the flows in situations like
these.  Might even be the difference in a tank size or an extra tank when
dealing with multiples.  50 psi would be more typical in these parts of the
country.

So throw in a sometimes and I'll go along with most of what you said.
Except the clogging part.  It's the RTI and linkage moving out of the way
that would be the problem with paint build up.  I don't see orifice size
being a factor here.    


Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, June 15, 2009 1:41 PM
To: [email protected]
Subject: RE: Mixing k-factors in paintspray booths

If you're trying to save a few gpm by going with the smaller orifice, it's
really not worth the effort.  Plus unless you're bagging the heads, smaller
orifice is more likely to get clogged sooner than larger orifice from the
spraying effort.  In addition, depending on the hazard you're protecting, a
little cushion on the discharge side may not be a bad thing.  No need to
shave the hydraulics that close.  When heads get covered and need to be
replaced, the smaller orifice probably won't be noticed and the head will be
replaced with a standard 5.6 anyway.  Keep it simple.   

What is the key material being sprayed?


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Randy Knutson
Sent: Monday, June 15, 2009 1:42 PM
To: [email protected]
Subject: Mixing k-factors in paintspray booths

Forum Members,

 

Can I use a smaller k-factor sprinkler in the pit and exhaust plenum of a
paint spray booth?

Due to the geometry of the pit and exhaust plenum. The sprinklers in there
are covering about 36 square feet per sprinkler.

Any insight would be appreciated.

 

Randy Knutson

Shilo Automatic Sprinkler, Inc.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to