What Craig said.

There's information in ASCE7 and the IBC that will help you determine 
whether or not your project is required to follow the rules for seismic 
protection, which is considerably more extensive than just bracing.

And there are no more seismic zones, it's now based on information 
regarding the position of the site relative to faults or seismic 
activity areas, and there is important data from the USGS (available 
free on their website) necessary to determine those values.

In short, what you're looking to determine is the "Seismic Design 
Category", which is designated as A through F.

In category A and B there are no requirements for seismic protection of 
sprinkler systems.

In category C the protection requirements are based on complying with 
the information in the '02 edition of NFPA-13

In category D and E you must follow the requirements of ASCE7 with 
respect to horizontal force and pipe displacement, which can be achieved 
by following the guidelines in the '07 edition of NFPA-13.

In category F you may as well buy some kind of rubber isolators because 
you're floating on mud.  Well, maybe not quite, but the civil and 
structural engineers for the project are already going to be well aware 
of the conditions and will most likely give you some excellent guidance 
on what to do.

Chapters 11 and 13 of ASCE7-05, and section 1613 of the '06 IBC contain 
somewhat identical information on how to determine the seismic design 
category.
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
IMPORTANT NOTICE: This correspondence is not a Formal Interpretation 
issued pursuant to NFPA Regulations. Any opinion expressed is the 
personal opinion of the author and does not necessarily represent the 
official position of the NFPA or its Technical Committees. In addition, 
this correspondence is neither intended, nor should it be relied upon, 
to provide professional consultation or services.


Phil Nawrocki wrote:
> We are in Phoenix, seismic zone #1.
>
> Regards,
> Phillip H. Nawrocki
> Design Manager
> National Fire Sprinkler, Inc.
> 1544 W. Grant St.
> Phoenix, AZ 85007-3314
> (602) 712-1180 Phone  Ext #33
> (602) 712-1260 Fax
> [email protected]
> Fire Sprinklers Save Lives!
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Jay White
> Sent: Thursday, June 18, 2009 6:24 AM
> To: [email protected]
> Subject: RE: Seismic Protection
>
> Are you in a seismic zone?
>
>
> Jay White
> Estimator/Design Manager
> Dynamic Fire Protection
> 1807 Hwy. 25 South
> Starkville, MS 39759
> Phone: 662-324-1550
> Fax: 662-324-1545
> Cell: 662-312-2426
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Phil 
> Nawrocki
> Sent: Thursday, June 18, 2009 8:07 AM
> To: [email protected]
> Subject: Seismic Protection
>
> Good Morning. We would like to know what determines when seismic
> protection is required in buildings. We know NFPA #13 tells us how to
> install the protection, but not when it is required. Thank you.
>
>
>
> Regards,
>
> Phillip H. Nawrocki
> Design Manager
> National Fire Sprinkler, Inc.
> 1544 W. Grant St.
> Phoenix, AZ 85007-3314
> (602) 712-1180 Phone Ext #33
> (602) 712-1260 Fax
> [email protected]
> Fire Sprinklers Save Lives!
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to