Another interesting condition that can increase the seismic design
requirements are the types of soils your building on. Even in an area with a
very low level of seismic activity, that can be magnified by the soils, kind
of a counter dampening effect. This is most often seen in swampy and river
bottom areas. The problem is with all the development of the past 100 years,
some traditionally "Swamps" are now down town urban areas like D.C. So the
soils testing becomes a factor in the seismic design category selection. I
call this the "Bowl of Jell-O" effect, it only takes a little motion to get
it going, but then it just seems to keep on moving on its own.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
ParsleyConsulting
Sent: Thursday, June 18, 2009 8:23 AM
To: [email protected]
Subject: Re: Seismic Protection

What Craig said.

There's information in ASCE7 and the IBC that will help you determine
whether or not your project is required to follow the rules for seismic
protection, which is considerably more extensive than just bracing.

And there are no more seismic zones, it's now based on information regarding
the position of the site relative to faults or seismic activity areas, and
there is important data from the USGS (available free on their website)
necessary to determine those values.

In short, what you're looking to determine is the "Seismic Design Category",
which is designated as A through F.

In category A and B there are no requirements for seismic protection of
sprinkler systems.

In category C the protection requirements are based on complying with the
information in the '02 edition of NFPA-13

In category D and E you must follow the requirements of ASCE7 with respect
to horizontal force and pipe displacement, which can be achieved by
following the guidelines in the '07 edition of NFPA-13.

In category F you may as well buy some kind of rubber isolators because
you're floating on mud.  Well, maybe not quite, but the civil and structural
engineers for the project are already going to be well aware of the
conditions and will most likely give you some excellent guidance on what to
do.

Chapters 11 and 13 of ASCE7-05, and section 1613 of the '06 IBC contain
somewhat identical information on how to determine the seismic design
category.
--
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued
pursuant to NFPA Regulations. Any opinion expressed is the personal opinion
of the author and does not necessarily represent the official position of
the NFPA or its Technical Committees. In addition, this correspondence is
neither intended, nor should it be relied upon, to provide professional
consultation or services.


Phil Nawrocki wrote:
> We are in Phoenix, seismic zone #1.
>
> Regards,
> Phillip H. Nawrocki
> Design Manager
> National Fire Sprinkler, Inc.
> 1544 W. Grant St.
> Phoenix, AZ 85007-3314
> (602) 712-1180 Phone  Ext #33
> (602) 712-1260 Fax
> [email protected]
> Fire Sprinklers Save Lives!
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Jay 
> White
> Sent: Thursday, June 18, 2009 6:24 AM
> To: [email protected]
> Subject: RE: Seismic Protection
>
> Are you in a seismic zone?
>
>
> Jay White
> Estimator/Design Manager
> Dynamic Fire Protection
> 1807 Hwy. 25 South
> Starkville, MS 39759
> Phone: 662-324-1550
> Fax: 662-324-1545
> Cell: 662-312-2426
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Phil 
> Nawrocki
> Sent: Thursday, June 18, 2009 8:07 AM
> To: [email protected]
> Subject: Seismic Protection
>
> Good Morning. We would like to know what determines when seismic 
> protection is required in buildings. We know NFPA #13 tells us how to 
> install the protection, but not when it is required. Thank you.
>
>
>
> Regards,
>
> Phillip H. Nawrocki
> Design Manager
> National Fire Sprinkler, Inc.
> 1544 W. Grant St.
> Phoenix, AZ 85007-3314
> (602) 712-1180 Phone Ext #33
> (602) 712-1260 Fax
> [email protected]
> Fire Sprinklers Save Lives!
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to