I don't know of any restrictions in code or standards that would preclude a "central plant" water supply, and I think the AHJ is over-reaching in his interpretation of separate. NFPA 13 and 14 speak to connection of systems to adequate water supplies, which can take any one of a number of forms. Those can even be a combination elements - tanks, pumps, wells - that collectively make up an adequate water supply. The "separate and complete stand-alone fire suppression system" is still to be furnished: separate service from the point of connection to the water supply, separate control valve(s) and FDC(s), separate riser, separate local alarm, separate supervisory system, separate monitoring address, etc. So long as the existing automatic water supply is adequate to meet whatever demands are created in the new building, there's no prohibition against using it.
Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Mike Hairfield Sent: Saturday, June 20, 2009 6:46 AM To: AFSA SprinklerFORUM Subject: Fire Pump for Multiple Buildings Existing facility has one fire pump serving two existing buildings, the owner wants to add a third building. Local AHJ states IBC requires a separate complete stand alone fire suppression system thus requiring the owner to provide a new fire pump and city water connection for the building. Has any one run across this IBC requirement or is the AHJ incorrect in his statement? Mike Hairfield _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4173 (20090620) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 4173 (20090620) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)