Steve,

Good practice says you shouldn't feed more than one building from a
riser but is there a reference from IBC that clearly states that? I
agree that one pump can service several buildings on a campus (as long
as it's in a separated pump house) just as a single pump can feed
several risers in the same building or a municipal pump can service
multiplke properties wuthin a water district.

On Sat, Jun 20, 2009 at 9:51 AM, Steve Leyton<[email protected]> wrote:
> I don't know of any restrictions in code or standards that would
> preclude a "central plant" water supply, and I think the AHJ is
> over-reaching in his interpretation of separate.   NFPA 13 and 14 speak
> to connection of systems to adequate water supplies, which can take any
> one of a number of forms. Those can even be a combination elements -
> tanks, pumps, wells - that collectively make up an adequate water
> supply.  The "separate and complete stand-alone fire suppression system"
> is still to be furnished:  separate service from the point of connection
> to the water supply, separate control valve(s) and FDC(s), separate
> riser, separate local alarm, separate supervisory system, separate
> monitoring address, etc.   So long as the existing automatic water
> supply is adequate to meet whatever demands are created in the new
> building, there's no prohibition against using it.
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Mike
> Hairfield
> Sent: Saturday, June 20, 2009 6:46 AM
> To: AFSA SprinklerFORUM
> Subject: Fire Pump for Multiple Buildings
>
>
>
>  Existing facility has one fire pump serving two existing buildings, the
> owner wants to
>
> add a third building. Local AHJ states IBC requires a separate complete
> stand alone
>
> fire suppression system thus requiring the owner to provide a new fire
> pump and city
>
> water connection for the building.
>
>
>
> Has any one run across this IBC requirement or is the AHJ incorrect in
> his statement?
>
>
>
> Mike Hairfield
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4173 (20090620) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4173 (20090620) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to