Last summer we grouped up to four separately deeded apt buildings to a common NFPA 20 fire pump. Got letters from an NFPA 20 and an NFPA 13 committee member in support of the concept. This overcame the City's original objection.
The City DID require deed restrictions that negated a sale if the unit being sold off from common ownership hadn't had an appropriate water supply installed prior to the sale. Yes, I met the committee members at Convention.......might have furnished them a preemptive refreshment for just that type of moment. You are absolutely within the Committees' intent to supply multiple buildings and systems from one fire pump. As Chris points out, any nearby industrial complex could be held up as an example and may spare you having to track down letters if the AHJ has an "AHA!' moment when hearing the corollary. glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Mak Sent: Saturday, June 20, 2009 7:15 PM To: [email protected] Subject: Re: Fire Pump for Multiple Buildings Tel the AHJ to consider any industrial plant such as a steel mill or similar. Would he expect to see multiple pumps (and storage tanks) for each protected building? We have a steel mill around an hour south of us that has somewhere in the order of 50 to 100 sprinkler and deluge systems. Obviously, one water supply, with two reservoirs and two or three pumps. If your AHJ was right, the only people that would be happy would be the pump manufactures. Regards Chris Mak Sprinkler Certification Manager Aon New Zealand Level 1, 4 Fred Thomas Drive,, Takapuna DDI: +64 9 486 9761 | Mobile:027 434 4058 | Fax:+64 9 486 0112 Ron Greenman <rongreen...@gmai l.com> To Sent by: [email protected] sprinklerforum-bo cc un...@firesprinkl er.org Subject Re: Fire Pump for Multiple Buildings 21/06/2009 11:09 a.m. Please respond to sprinklerfo...@fi resprinkler.org Yes, we are agreeing. On Sat, Jun 20, 2009 at 12:46 PM, <[email protected]> wrote: > NFPA 13 contains the "1 riser for each building" reference, and 2007 includes an exception for buildings connected by attached construction, such as a covered walkway or breezeway. I think we're agreeing, no? So long as the 3rd building has its own system, you can use the common water supply ... > > > > Sent from my Verizon Wireless BlackBerry > > -----Original Message----- > From: "Ron Greenman" <[email protected]> > > Date: Sat, 20 Jun 2009 11:58:04 > To: <[email protected]> > Subject: Re: Fire Pump for Multiple Buildings > > > Steve, > Good practice says you shouldn't feed more than one building from a > riser but is there a reference from IBC that clearly states that? I > agree that one pump can service several buildings on a campus (as long > as it's in a separated pump house) just as a single pump can feed > several risers in the same building or a municipal pump can service > multiplke properties wuthin a water district. > On Sat, Jun 20, 2009 at 9:51 AM, Steve Leyton<[email protected]> wrote: >> I don't know of any restrictions in code or standards that would >> preclude a "central plant" water supply, and I think the AHJ is >> over-reaching in his interpretation of separate. NFPA 13 and 14 speak >> to connection of systems to adequate water supplies, which can take any >> one of a number of forms. Those can even be a combination elements - >> tanks, pumps, wells - that collectively make up an adequate water >> supply. The "separate and complete stand-alone fire suppression system" >> is still to be furnished: separate service from the point of connection >> to the water supply, separate control valve(s) and FDC(s), separate >> riser, separate local alarm, separate supervisory system, separate >> monitoring address, etc. So long as the existing automatic water >> supply is adequate to meet whatever demands are created in the new >> building, there's no prohibition against using it. >> >> Steve Leyton >> Protection Design & Consulting >> San Diego, CA >> >> >> >> >> -----Original Message----- >> From: [email protected] >> [mailto:[email protected] < mailto:[email protected]> ] On Behalf Of Mike >> Hairfield >> Sent: Saturday, June 20, 2009 6:46 AM >> To: AFSA SprinklerFORUM >> Subject: Fire Pump for Multiple Buildings >> >> >> >> Existing facility has one fire pump serving two existing buildings, the >> owner wants to >> >> add a third building. Local AHJ states IBC requires a separate complete >> stand alone >> >> fire suppression system thus requiring the owner to provide a new fire >> pump and city >> >> water connection for the building. >> >> >> >> Has any one run across this IBC requirement or is the AHJ incorrect in >> his statement? >> >> >> >> Mike Hairfield >> _______________________________________________ >> Sprinklerforum mailing list >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum < http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> >> For Technical Assistance, send an email to: >> [email protected] >> >> To Unsubscribe, send an email >> to:[email protected] >> (Put the word unsubscribe in the subject field) >> >> >>__________ Information from ESET NOD32 Antivirus, version of virus >> signature database 4173 (20090620) __________ >> >> The message was checked by ESET NOD32 Antivirus. >> >> http://www.eset.com <http://www.eset.com> >> >> >> >>__________ Information from ESET NOD32 Antivirus, version of virus >> signature database 4173 (20090620) __________ >> >> The message was checked by ESET NOD32 Antivirus. >> >> http://www.eset.com <http://www.eset.com> >> >> _______________________________________________ >> Sprinklerforum mailing list >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum < http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email to:[email protected] >> (Put the word unsubscribe in the subject field) >> > > > -- > Ron Greenman > at home.... > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum < http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > For Technical Assistance, send an email to: [email protected] > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > __________ Information from ESET NOD32 Antivirus, version of virus signature database 4173 (20090620)__________ > The message was checked by ESET NOD32 Antivirus. > http://www.eset.com <http://www.eset.com> > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) This document should only be read by those persons to whom it is addressed and is not intended to be relied upon by any person without subsequent written confirmation of its contents. Accordingly, our company disclaim all responsibility and accept no liability (including in negligence) for the consequences for any person acting, or refraining from acting, on such information prior to the receipt by those persons of subsequent written confirmation. If you have received this e-mail message in error, please notify us immediately by telephone. Please also destroy and delete the message from your computer. The Unsolicited Electronic Message Act 2007 (The Spam Act) came into effect from 5 September 2007. As a valued client you may receive communications from us from time to time, including electronic publications, invitations and related information. Please advise if you wish us to stop sending these communications to you. Otherwise we will assume you wish to continue receiving these communications from us. Any form of reproduction, dissemination, copying, disclosure, modification, distribution and/or publication of this e-mail message is strictly prohibited. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)