George,

Thank you, well worth reading.

Frans Stoop

At 14:12 17-6-2009 -0400, you wrote:
>Damien-
>I'd highly recommend you:
>
>1. Read James G's white paper "Variables that affect the Performance 
>of Dry Pipe Systems" at
>http://www.tyco-fire.com/index.php?P=show&id=DryPipeSystems_Rev&B=&BK=archive_news
>
>2. Look into obtaining FDT calculation software to either prove your
>systems' ability to meet the water delivery requirements, or what you can
>save, or what you can change to make them work. www.stinkcad.com
>Ok, just kidding, my plugs come with a sense of humor-
>http://www.sprinkcad.com/sprinkfdt.php There, now there's no chance this
>plug will get me a discount on the SprinkCAD seat I ordered yesterday. No,
>we're not abandoning our friends in NH.
>
>We've had HUGE systems that delivered water in a fraction of what would have
>been expected, far faster than NFPA requires.
>
>Low pressure will allow water to be diverted into non-flowing branchlines.
>Its really obvious when you watch the results of a system tripping and then
>watch the water go up the lines and mains not flowing, then change the gas
>pressure and see the changes possible.
>
>You may, depending on the AHJ, be able to not wait until a field test to see
>if you really only needed 5 risers or if you needed 12. or if even 12
>wouldn't help cause bulk mains eat up all your time.
>
>The problem is, without the software you just don't know. And not knowing
>until the acceptance test is a really stupid way to determine your needs
>when the answers are available before steel goes up.
>
>We were up at their Tech Center last week and I gotta tell you, the stuff is
>amazing.
>
>Yes, there is certainly a sweet spot in the gas pressure settings. And those
>are far easier to determine on a pc than in the field when its too late to
>change the piping, or find out maybe you could have installed a few less
>valves.
>
>glc
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Damien
>Shannon
>Sent: Wednesday, June 17, 2009 12:55 PM
>To: [email protected]
>Subject: RE: Slow responding dry pipe valves
>
>Frans,
>
>Very curious to know how you got on with the Victaulic valve w/ 1300 gallons
>to make the 60 sec requirement after making the adjustments discussed (or
>anywhere close). I need to do a building with 8 dry systems (new
>construction) that requires all the valves at a main header. The bulk main
>to the actual area of protection for some of the systems is forcing capacity
>well beyond 750 gallons (approx 900). The client originally was going with
>Victaulic valves, based on the premise that the lower air pressure would
>lead to less air to be exhausted prior to water being discharged.
>Trying to find out if there's a 'sweet spot' where the low air pressure
>versus 'higher pressure' Dry Pipe valves work best.
>Thank you for any insight you can provide.
>
>Damien Shannon
>QED Sprinkler Designs Inc.
>(773) 704 2571
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Frans Stoop
>Sent: Tuesday, April 28, 2009 8:25 PM
>To: [email protected]
>Subject: Slow responding dry pipe valves
>
>Dear colleagues,
>
>Our client has a rather large dry pipe system supplied by a Victaulic
>dry pipe valve complete with an accelerator.
>The system responds to slow to the ITC: more than 3 minutes.
>The contents of the system is approx. 1300 gallon.
>The air pressure in the system was set lower (in compliance with the
>Victaulic installation sheets) than we are used to with dry pipe
>valves of other manufacturers.
>
>The sprinkler contractor and the local Victaulic representative
>couldn't find the cause yet.
>My personal impression is that the Victaulic mat take much more time
>between opening the test valve and water delivery than dry pipe
>valves of other brands.
>Does anyone share this impression or had the same experience ? If you
>prefer, you may react off-forum.
>
>Frans Stoop
>TOS architecture & fire protection
>Netherlands <[email protected]>
>Tel. +31-24-324 0112
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to