Thanks again for your responses! An exhauster might be difficult to get, as Roland pointed out. And I agree with you, Ron, they are a maintenance nightmare. However, Tyco Europe still has Star exhausters in their on-line catalog.
Dave: 50 seconds is still to long indeed. We will put the air maintenance device on the check list. Maybe the orifice is missing or the bypass valve left open. Rodney: We will thoroughly check the accelerator. Scot: Moving the dry pipe valve closer to the protected area and feeding it by a traced and isolated wet mains would be an ultimate solution. Also splitting the area into two smaller areas, using 2 dry pipe valves and feeding the smaller areas with 2 dry headers is not our first choice. We still think something is not operating the way it should. Thom: OK, thanks to your "picture" I can imagine that a high pressure system can be quicker than a low pressure system. At first I thought that it wouldn't make a difference because all air pressures in the Victaulic system are relative. The "picture" also leads to another suggested cause: We found distribution piping in the system, branching off the header, that could not be drained. When the IT is opened in an area at the end of the header, the compressed air at the end of this distribution branch can expand and press the remaining water (think of upto 10 gallon) back in the header. Thus blocking the way out for air in the header and slowing the air discharge down. We have a lot of items to check now. It will take a while before we can investigate and test again. It needs some planning first. (To remind you: draining this system takes 2 people half a day!) I'll keep you informed. Frans Stoop TOS architecture & fire protection Netherlands <[email protected]> Tel. +31-24-324 0112 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)