would not the pressure from the water, rather than the air, determinemore
accurately what is happening during water-filling-and-air-purging?

if water is coming in at 7psig, ignoring the complications of filling dead
ends,
and velocity pressure vs normal pressure, and the expanding boundary marked
by the front of the water wave as it fills the pipe...

if water is coming in a 7 psig, will it not trap air in the branches at
close
to 7psig?  thus air is compressed 7: 1 in low pressure and compressed 7:2
in high-pressure systems.  This suggest that roughly double the amount
of water is needed to fill branches in low pressure systems than the amount
of water needed to fill branches in high pressure systems.  That might
explain
some of why the high pressure systems deliver water quicker,

although it does not explain the sweet spot.

scot deal
excelsior fire engineering




> For example: with a water pressure of 7 bar (100 psi)
> a low air pressure systems may trip at 1 bar (14 psi) and the standby
> pressure is 1.4 bar (20 psi),
> a high air pressure system may trip at 2 bar (28 psi) and the standby
> pressure is 2.8 bar (40 psi).
>
> So there is hardly any difference until the valve has tripped.
> After the valve has tripped, it is another situation:
> Water at a pressure of 7 bar (100 psi) is trying to fill-up a pipe
> system with a remaining amount of air in it that is different for
> both types of systems:
> remaining pressure in a low air pressure system: 1 bar (14 psi),
> remaining pressure in a high air pressure system: 2 bar (28 psi).
>
>
>