Damien,

I'm a little embarrased to tell you this, but besides slow responding 
dry pipe valves, we in Holland also have at least one slow responding 
sprinkler contractor.
The problem showed up in juli 2008. It is more than one month ago now 
that the subject was actual on the forum, and all that we have 
received up to now is a plan of approach that might at best start to 
be excuted within 3 weeks from now. I will keep you informed about the outcome.

Regarding the difference between low air pressure systems (like 
Victaulic) and high air pressure systems (like GEM and Viking), I see 
it like this:
Either the valve is operated by a latch with piston (Victaulic and 
others) or by a differtial pressure over the clapper (most common), 
you need a certain pressure to keep the latch in lock position and/or 
the clapper closed. Now most manufacturers add 30% for safety (may be 
required by FM).

For example: with a water pressure of 7 bar (100 psi)
a low air pressure systems may trip at 1 bar (14 psi) and the standby 
pressure is 1.4 bar (20 psi),
a high air pressure system may trip at 2 bar (28 psi) and the standby 
pressure is 2.8 bar (40 psi).

To release 30% of the air trough the ITC takes approximately the same 
amount of time in low and high air pressure systems.
The pressure follows an e-function along the time-axis.
(The accelerator might complicate this.)

So there is hardly any difference until the valve has tripped.
After the valve has tripped, it is another situation:
Water at a pressure of 7 bar (100 psi) is trying to fill-up a pipe 
system with a remaining amount of air in it that is different for 
both types of systems:
remaining pressure in a low air pressure system: 1 bar (14 psi),
remaining pressure in a high air pressure system: 2 bar (28 psi).

It is not difficult to see that the low air pressure system needs 
more water and time before water discharges from the ITC.
The low air pressure system requires more water in the branches 
before the pressure in the branches is in balance with the pressure 
in the distribution main.

I'm aware that there is much more to say about it, but I consider 
this as the main effect.

Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112

At 11:54 17-6-2009 -0500, you wrote:
>Frans,
>
>Very curious to know how you got on with the Victaulic valve w/ 1300 gallons
>to make the 60 sec requirement after making the adjustments discussed (or
>anywhere close). I need to do a building with 8 dry systems (new
>construction) that requires all the valves at a main header. The bulk main
>to the actual area of protection for some of the systems is forcing capacity
>well beyond 750 gallons (approx 900). The client originally was going with
>Victaulic valves, based on the premise that the lower air pressure would
>lead to less air to be exhausted prior to water being discharged.
>Trying to find out if there's a 'sweet spot' where the low air pressure
>versus 'higher pressure' Dry Pipe valves work best.
>Thank you for any insight you can provide.
>
>Damien Shannon
>QED Sprinkler Designs Inc.
>(773) 704 2571
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Frans Stoop
>Sent: Tuesday, April 28, 2009 8:25 PM
>To: [email protected]
>Subject: Slow responding dry pipe valves
>
>Dear colleagues,
>
>Our client has a rather large dry pipe system supplied by a Victaulic
>dry pipe valve complete with an accelerator.
>The system responds to slow to the ITC: more than 3 minutes.
>The contents of the system is approx. 1300 gallon.
>The air pressure in the system was set lower (in compliance with the
>Victaulic installation sheets) than we are used to with dry pipe
>valves of other manufacturers.
>
>The sprinkler contractor and the local Victaulic representative
>couldn't find the cause yet.
>My personal impression is that the Victaulic mat take much more time
>between opening the test valve and water delivery than dry pipe
>valves of other brands.
>Does anyone share this impression or had the same experience ? If you
>prefer, you may react off-forum.
>
>Frans Stoop
>TOS architecture & fire protection
>Netherlands <[email protected]>
>Tel. +31-24-324 0112
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)