Don't do NFPA 30 designs very often and this struck me as peculiar.  '08 -
16.6.1.6 and .7 clearly says to me anyway we don't have to calc the in-racks
and overhead simultaneously.   Seems a significant departure from normal.
So I am reading this right?  My only thought is there are so many heads in
the rack with a barrier we wouldn't expect the ceiling heads to operate?  I
do see the option when you leave out the barrier we are back to normal
balancing.  

 

Chris Cahill, P.E.

Fire Protection Engineer