That particular section is dealing with racks with internal barriers. The idea is that the in-racks will operate first and provide control if the fire originates within the racks. Ceiling sprinks operate for the top rack level or the open floor area including aisles. But even then the rack sprinkler will spill out into those spaces.
NFPA 30 has some real specific requirements for real specific items. Hopefully someone has done their homework on this. Determining protection schemes for flammable and combustibles is one of the easiest to screw up if you are not familiar with the commodity and storage arrangements. People have a tendency to skim through the info, make assumptions and not read the details. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Wednesday, July 01, 2009 10:35 AM To: [email protected] Subject: Scheme A NFPA 30 Don't do NFPA 30 designs very often and this struck me as peculiar. '08 - 16.6.1.6 and .7 clearly says to me anyway we don't have to calc the in-racks and overhead simultaneously. Seems a significant departure from normal. So I am reading this right? My only thought is there are so many heads in the rack with a barrier we wouldn't expect the ceiling heads to operate? I do see the option when you leave out the barrier we are back to normal balancing. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)