That particular section is dealing with racks with internal barriers. The idea 
is that the in-racks will operate first and provide control if the fire 
originates within the racks.  Ceiling sprinks operate for the top rack level or 
the open floor area including aisles.  But even then the rack sprinkler will 
spill out into those spaces.

NFPA 30 has some real specific requirements for real specific items.  Hopefully 
someone has done their homework on this.  Determining protection schemes for 
flammable and combustibles is one of the easiest to screw up if you are not 
familiar with the commodity and storage arrangements.  People have a tendency 
to skim through the info, make assumptions and not read the details.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Wednesday, July 01, 2009 10:35 AM
To: [email protected]
Subject: Scheme A NFPA 30

Don't do NFPA 30 designs very often and this struck me as peculiar.  '08 -
16.6.1.6 and .7 clearly says to me anyway we don't have to calc the in-racks
and overhead simultaneously.   Seems a significant departure from normal.
So I am reading this right?  My only thought is there are so many heads in the 
rack with a barrier we wouldn't expect the ceiling heads to operate?  I do see 
the option when you leave out the barrier we are back to normal balancing.  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to