Plus those design schemes relate to specific criteria as referenced from 
various Tables within NFPA 30.  They are not stand alone.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Wednesday, July 01, 2009 10:35 AM
To: [email protected]
Subject: Scheme A NFPA 30

Don't do NFPA 30 designs very often and this struck me as peculiar.  '08 -
16.6.1.6 and .7 clearly says to me anyway we don't have to calc the in-racks
and overhead simultaneously.   Seems a significant departure from normal.
So I am reading this right?  My only thought is there are so many heads in the 
rack with a barrier we wouldn't expect the ceiling heads to operate?  I do see 
the option when you leave out the barrier we are back to normal balancing.  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to