There are quite a few parameters that need to be in place to apply Scheme A.  
But, with those satisfied, you do essentially ignore the overhead demand / 
balance you'd normally encounter.

Anytime I've applied Scheme A for rack set ups, it's also been fed from it's 
own riser, or an adjacent system - as the AHJ has allowed.

So, as long as you're good to go on the barriers and other parameters, get the 
8.0's to push 50psi each and you're golden.



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Wednesday, July 01, 2009 10:35 AM
To: [email protected]
Subject: Scheme A NFPA 30

Don't do NFPA 30 designs very often and this struck me as peculiar.  '08 -
16.6.1.6 and .7 clearly says to me anyway we don't have to calc the in-racks
and overhead simultaneously.   Seems a significant departure from normal.
So I am reading this right?  My only thought is there are so many heads in
the rack with a barrier we wouldn't expect the ceiling heads to operate?  I
do see the option when you leave out the barrier we are back to normal
balancing.



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: [email protected]



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to