Right or wrong I always reconciled 13 vs. 72 like this.  The flow switch
must activate within the parameters of 13.  5 minutes.  Once the paddle
moves and the electrical connection is made 72 takes over and the FA must
respond within the parameters of 72.  90 seconds.  So in theory 6.5 minutes
could pass between opening the inspectors test valve and the alarm signal
engaging in the FAP.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Wednesday, July 15, 2009 10:14 AM
To: [email protected]
Subject: RE: water flow timing

NFPA 72 5.11.2 says within 90 seconds.  

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: Geoff Dyce [mailto:[email protected]] 
Sent: Wednesday, July 15, 2009 7:55 AM
To: [email protected]
Subject: water flow timing

We are having a discussion regarding time required for water flow
notification.  One party says on a wet system, there is no particular time
requirement.  Another party says there is a time limitation.  What say you
all???

Thanks in advance.

 

Geoffrey H. Dyce

Operations Manager/NICET IV

DELTA Fire Sprinklers, Inc.

A Vetran Owned Small Business

Ph:  407-328-3000 ext 143

Fx:  407-575-9991

E-Mail:  [email protected]

 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to