NFPA 13:

6.9.4.1 Electrically operated alarm attachments forming part of an
auxiliary, central station, local protective, proprietary, or remote station
signaling system shall be installed in accordance with NFPA 72R, National
Fire Alarm CodeR.

 

NFPA 72:

5.10 Sprinkler Waterflow Alarm-Initiating Devices.

5.10.1* The provisions of Section 5.10 shall apply to devices that initiate
an alarm indicating a flow of water in a sprinkler system.

5.10.2* Initiation of the alarm signal shall occur within 90 seconds of
waterflow at the alarm-initiating device when flow occurs that is equal to
or greater than that from a single sprinkler of the smallest orifice size
installed in the system.

 

A.5.10.2 The waterflow device should be field adjusted so that an alarm is
initiated no more than 90 seconds after a sustained flow of at least 40
L/min (10 gpm). Features that should be investigated to minimize alarm
response time include the following:

(1) Elimination of trapped air in the sprinkler system piping

(2) Use of an excess pressure pump

(3) Use of pressure drop alarm-initiating devices

(4) A combination thereof

 

I have attached the applicable requirements above for reference (NFPA 2002
Edition). For electronic fire alarms, the alarm device should activate
within a maximum of 90 seconds after water flow of 10 gpm or more occurs at
the alarm initiating device. For wet systems, the industry standard is to
ensure electronic water flow alarms within 90 seconds of a fully open
Inspector's Test Connection. This is really not difficult to accomplish as
long as the system does not have large pockets of trapped air. Remove the
air, as outlined in Section A.5.10.2(1), and set the delay for 45-60
seconds; alarm activates <90 seconds and there are no false alarms.

 

Chris used his example to show how much smarter he is than the "FM Guy", but
he failed to mention that he had no idea why the system required 58 seconds
for the electronic water flow switch to activate. If a wet system is full
(or close to full of water), the water flow switch activates almost
immediately when the Inspector's Test Connection is opened. Sprinkler system
people with several years of experience in the field know this to be true
regardless of the size of the system. If a wet system has significant
pockets of trapped air, the decompression of the air pockets results in a
significant delay prior to the initial activation of the flow switch. The
pockets of trapped air will typically result in a cycling waterflow switch
and other serious issues as well. If the flow switch in Chris's example
cycled too quickly, his 45 second delay probably created a code violation (I
have seen several waterflow switches cycle for 10-15 minutes without ever
activating the alarm => remove air pockets and the problem is resolved). I
realize this is a rather harsh comment, but I personally think Chris and the
"FM Guy" did not help the customer very much. I wonder if the system still
has trapped air pockets and all of the issues/problems which are caused by
large pockets of air in wet sprinkler systems? Oh yeah, I almost forgot,
someone stated that the alarm issues are strictly for the alarm company
employees....maybe it should be their responsibility to remove the air
pockets! 

 

I do not know where to begin with the 6.5 minute requirement referenced by
Chris. This is very misleading and I would strongly suggest against applying
this logic in the real world. NFPA 13 allows up to 5 minutes for the local
waterflow alarms to activate; however, this does not apply to the electronic
alarm devices. NFPA 13 indicates all electronic waterflow alarm devices
shall comply with the applicable portions of NFPA 72. The 5 minute
requirement allows multiple retard chambers and other delays to prevent
nuisance water motor gong alarms. The NFPA 13 & NFPA 72 requirements are
based on wet systems which are full or close to full of water; therefore, it
is simply illogical to accept the premise that waterflow would occur at the
sprinkler riser 1-5 minutes after the Inspector's Test Connection was
opened. Imagine a 10 in. diameter section of pipe 2 miles long with 90
degree elbows on each end facing upward. If the section of pipe was 100%
full of water and you poured a 5 gallon pail of water in one end, the water
would overflow immediately at the far end! Same thing only we are dealing
with a smaller volume.

 

I have resolved this exact waterflow switch alarm problem more times than I
care to remember; it is so common that I think I am in the early stages of a
Crusade to inform our industry. I have also obtained indisputable facts
regarding the excess pressure development in sprinkler systems due to
trapped air pockets. I have identified and resolved the excessive pressure
problem (due to air in the system) 17 times this year alone! Most of these
systems had >300 psi in the afternoon and 60-150 psi (depending on the
static water supply) during the morning hours. Remove the trapped air and
the pressure fluctuations are gone. Give me a call if anyone is truly
interested and I will send you the data from my electronic data logger (I
log the wet sprinkler system pressure; every 30 seconds for 7 days). We can
all learn from each others experiences as long as we all maintain an open
minded approach.

 

I hope this information is beneficial to someone out there!

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

From: "Chris Cahill" <[email protected]>

Subject: RE: water flow timing

To: <[email protected]>

Message-ID: <91f4ffce394b4f71bea941947a42a...@chris2005>

Content-Type: text/plain;     charset="us-ascii"

 

LOL,  1-Doesn't mean I'm not here. 2-Doesn't mean I'm wrong. 3-My scope of

work is 13, sounds like the FA guy's problem.

 

Seriously though it has only come up once that I have been part of in the

private sector.  After a long discussion on site the FM made us set the

retard on the flow switch so that the alarms rang in 60 seconds.  We could

see the meter spin with surges in the street and our pressure climb 20 psi

in a couple minutes.  It was a very large system (3" bl and 6" and 8" mains)

and took 58 seconds for the flow switch to even move. 1/2" head ITV because

of the office parts.   He was happy when we passed at 60 sec. with no

retard.  I advised him he created a situation that would result in false

alarms.  Of course he knew more than me.  5-10 minutes later BS'ing in the

parking lot sure enough the FD was dispatched for a flow alarm.  He was on

the VFD and his pager went off for the building he was at.  Priceless and

yes I did point out the "I told you so" as I left it in his "capable" hands,

he was a @#$^$%&$...@#.  I win after 3 more false alarms over the weekend and

they set the retard back to 45 seconds.   

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

-----Original Message-----

From: [email protected]

[mailto:[email protected]] On Behalf Of Thomas Watt

Sent: Wednesday, July 15, 2009 11:12 AM

To: [email protected]

Subject: Re: water flow timing

 

Chris, you would be butting heads with every AHJ in the Central Florida 

area. I have never gotten a CO without sounding alarms within 60-90 secs.

 

Thomas Watt

 

 

 

 

----- Original Message ----- 

From: "Chris Cahill" <[email protected]>

To: <[email protected]>

Sent: Wednesday, July 15, 2009 11:53 AM

Subject: RE: water flow timing

 

 

> Right or wrong I always reconciled 13 vs. 72 like this.  The flow switch

> must activate within the parameters of 13.  5 minutes.  Once the paddle

> moves and the electrical connection is made 72 takes over and the FA must

> respond within the parameters of 72.  90 seconds.  So in theory 6.5 

> minutes

> could pass between opening the inspectors test valve and the alarm signal

> engaging in the FAP.

> 

> Chris Cahill, P.E.

> Fire Protection Engineer

> Sentry Fire Protection, Inc.

 

 

Date: Wed, 15 Jul 2009 10:53:59 -0500

From: "Chris Cahill" <[email protected]>

Subject: RE: water flow timing

To: <[email protected]>

Message-ID: <8d141ac0c9c645fab97b4aeb7ff6a...@chris2005>

Content-Type: text/plain;     charset="us-ascii"

 

Right or wrong I always reconciled 13 vs. 72 like this.  The flow switch

must activate within the parameters of 13.  5 minutes.  Once the paddle

moves and the electrical connection is made 72 takes over and the FA must

respond within the parameters of 72.  90 seconds.  So in theory 6.5 minutes

could pass between opening the inspectors test valve and the alarm signal

engaging in the FAP.  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

-----Original Message-----

From: [email protected]

[mailto:[email protected]] On Behalf Of Jim Johnston

Sent: Wednesday, July 15, 2009 10:14 AM

To: [email protected]

Subject: RE: water flow timing

 

NFPA 72 5.11.2 says within 90 seconds.  

 

Jim Johnston, P.E.

Fire Protection Engineer

Inland Fire Protection, Inc

1100 Ahtanum Road

Yakima, WA 98903

Phone 509-248-4471

Fax 509-248-1180

[email protected]

 

 

-----Original Message-----

From: Geoff Dyce [mailto:[email protected]] 

Sent: Wednesday, July 15, 2009 7:55 AM

To: [email protected]

Subject: water flow timing

 

We are having a discussion regarding time required for water flow

notification.  One party says on a wet system, there is no particular time

requirement.  Another party says there is a time limitation.  What say you

all???

 

Thanks in advance.

 

 

 

Geoffrey H. Dyce

 

Operations Manager/NICET IV

 

DELTA Fire Sprinklers, Inc.

 

A Vetran Owned Small Business

 

Ph:  407-328-3000 ext 143

 

Fx:  407-575-9991

 

E-Mail:  [email protected]

 