If you are just ringing a bell for compliance with 13 it is 5 minutes
If you are activating alarms in accordance with 72 it is 90 seconds
local alarm = 5 minutes
Fire alarm system  = 90 seconds

Retards on flowswitches are limited to 90 seconds by UL

Regards,

mike

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Wednesday, July 15, 2009 10:24 AM
To: [email protected]
Subject: RE: water flow timing

And since both NFPA 13 and 14 refer (generally) to alarms in terms of
NFPA 72, that's the superseding criterion, methinks.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim
Johnston
Sent: Wednesday, July 15, 2009 8:14 AM
To: [email protected]
Subject: RE: water flow timing

NFPA 72 5.11.2 says within 90 seconds.  

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: Geoff Dyce [mailto:[email protected]] 
Sent: Wednesday, July 15, 2009 7:55 AM
To: [email protected]
Subject: water flow timing

We are having a discussion regarding time required for water flow
notification.  One party says on a wet system, there is no particular
time
requirement.  Another party says there is a time limitation.  What say
you
all???

Thanks in advance.

 

Geoffrey H. Dyce

Operations Manager/NICET IV

DELTA Fire Sprinklers, Inc.

A Vetran Owned Small Business

Ph:  407-328-3000 ext 143

Fx:  407-575-9991

E-Mail:  [email protected]

 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4246 (20090715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4246 (20090715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to