Mine were all 2 miles or greater

At 02:06 PM 8/26/2009, you wrote:
>We did one last year since the nearest 3-phase was down at the bottom of the
>mountain and it was $150k to bring it up the hill. So we were limited to a
>little- 10 or 15 sounds right-HP single phase as our supply, squeeked it
>out. But you see why we didn't really have the option to go 3-phase, next
>option economically was a diesel.
>
>glc
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Wednesday, August 26, 2009 1:34 PM
>To: [email protected]
>Subject: RE: 3 from 1
>
>The biggest single phase fire pump available has a 15 hp motor. Have
>done 3 of them and the power companies have been OK with it.
>
>
>At 12:33 PM 8/26/2009, you wrote:
> >Most utility companies have a maximum Hp they allow for single Ph power,
> >locally it is max 10 Hp. Not much advantage to a phase converter if your
> >only allowed 10Hp of single phase to supply it. I don't think a converter
> >can give you "soft start" capability.
> >
> >Thom McMahon, SET
> >Firetech, Inc.
> >2560 Copper Ridge Dr
> >P.O. Box 882136
> >Steamboat Springs, CO 80488
> >Tel:  970-879-7952
> >Fax: 970-879-7926
> >
> >
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of
> >[email protected]
> >Sent: Wednesday, August 26, 2009 10:30 AM
> >To: [email protected]
> >Subject: Re: 3 from 1
> >
> >
> >Also, the 2010 edition of NFPA 20 will explicitly state that you cannot
> >convert from single to three phase. (according to an NFSA bulletin the
> >committee has already agreed on this).
> >
> >
> >
> >Forest Wilson
> >
> >Cherokee Fire
> >
> >
> >-----Original Message-----
> >From: Ron Greenman <[email protected]>
> >To: [email protected]
> >Sent: Wed, Aug 26, 2009 12:26 pm
> >Subject: Re: 3 from 1
> >
> >
> >
> >
> >Todd,
> >
> >20-A.9.2.2 in the 2007 edition. Not prohibited but not recommended.
> >
> >On Wed, Aug 26, 2009 at 9:12 AM, Todd Williams<[email protected]> wrote:
> > > You may need to have an electrical engineer review the installation.
> > > I did a single phase pump a few years ago and ran into electrical
> > > problems (for which I was blamed). Hired an EE and he went through and
> > > found the electrician messed up the installation from the service
> > > right through to the pump as well as the generator feed and
> > > connection. Didn't have a converter, but did have two transformers
> > > because the electrician told us the wrong voltage (208 v. 240 - for
> > > which I was also blamed).
> > >
> > > BTW, what section of the Code says Phase Converters are not allowed?
> > > I couldn't find that at the time, but had rejected the idea anyway.
> > >
> > >
> > >
> > >
> > > At 11:58 AM 8/26/2009, you wrote:
> > >>I need some education of Phase Converters.
> > >>
> > >>
> > >>
> > >>A 300 gpm Fire Pump (Tank fed), is supplied by one of these things.
> > >>Single phase only is available, so one of these has been installed to
>make
> >it work.
> > >>Installed in '06-07ish, just replaced main board in controller. I was
> > >>there to do test following part replace. 240vac, dropped to 106-108
> > >>across the 3 as indicated on panel. Middle leg showed 422vac in event
>log,
> >as high peak.
> > >>When started, pump shaft (vertical) jumped up and down repeatedly. We
> > >>red tagged it and are waiting on word from electricians. Pump Motor
> > >>checked out fine. I know they are not allowed, but it was approved, so.,
>I
> >just test it.
> > >>
> > >>
> > >>
> > >>R/
> > >>
> > >>Matt
> > >>
> > >>
> > >>
> > >>Matthew J. Willis, CET
> > >>
> > >>Automatic Fire Sprinklers
> > >>
> > >>Norred Fire Systems L.L.C.
> > >>
> > >>318-387-1134 Voice
> > >>
> > >>318-387-1163 Facsimile
> > >>
> > >>[email protected]
> > >>
> > >>
> > >>
> > >>_______________________________________________
> > >>Sprinklerforum mailing list
> > >>[email protected]
> > >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > Todd G. Williams, PE
> > > Fire Protection Design/Consulting
> > > Stonington, Connecticut
> > > www.fpdc.com
> > > 860.535.2080
> > > ______________________
> >_________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> >
> >
> >
> >--
> >Ron Greenman
> >Instructor
> >Fire Protection Engineering
> >Bates Technical College
> >Tacoma, WA
> >
> >Member:
> >SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to