360 for sauna. If you decide to install in the non-comb steam room, remember that at sea level steam can only be 212'F without some type of pressure containment. At higher Altitudes it will be less than 212'F, so if you decide you need to protect this area, 286 is all you need for a steam room. (Corrosion is your biggest concern in a steam room)
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Knight Sent: Monday, September 14, 2009 10:21 AM To: [email protected] Subject: RE: 13D Sauna/Steam Rooms Thanks everybody for you input. 360 degree head it will be. Just to be sure though, this house has both a steam room and a sauna, use 360 d heads in both, right? BK _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)