Sorry. I kept writing 286 but meant 360. I'm either getting old or am
already there. I just can't remember which.

On Sat, Sep 12, 2009 at 9:47 AM, Thom McMahon <[email protected]> wrote:
> The maximum temp is a control setting the occupant can adjust. The emergency 
> setting is typically higher. The one I looked at last summer was 250'F. Was 
> it settable to a lower temp.? I don't know it just said max temp. 250 on it.
>
> Yes 360 is high, but how many btu's to raise the ceiling temp to 360 from 
> 194? How long to set head off? Seconds! Yes the occupant could receive burns 
> in those seconds, but I doubt their blood could boil, unless you raised the 
> temp 1 degree per minute or some such nonsense.
>
> 286'F heads discharge to a fire located 30 or more feet below them in a half 
> million Sf building in a couple of minutes. A 360'F head in a 1000 CF room 
> will react to a fire in seconds.
>
> We are fire protection, not slow electrical cooker protection. Life safety? 
> Horn strobe when temp exceeds 113'F, which I believe is the skin temp at 
> which everyone feels pain.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Forest Wilson
> Sent: Saturday, September 12, 2009 10:22 AM
> To: [email protected]
> Subject: Re: 13D Sauna/Steam Rooms
>
>
> From a website:
>
>  maximum allowable sauna temperature in Canada and the United States is 194°F 
> (90°C). These are C.S.A. and U.L. standards set back in 1982. At that time, 
> it was also mandated that there must be a high-temperature limit switch 
> within the sauna heater.
>
> ----
>
> Now, at 360*, in a 13D system, what is the priority: life or property 
> preservation?
>
> At 360* in a very small room the person's blood must be close to boiling. 
> Since the cut-off switch is a UL requirement, perhaps they have a paper on 
> sauna's with fire sprinklers.
>
>
>
> Forest Wilson
>
> Project Manager
> Cherokee Fire Protection Co.
> 3195 Dayton Xenia Rd Ste 900
> Dayton OH 45434
>
> ph: 937-376-2333
> fx: 614-455-4324
> cell: 937-307-5647
>
>
> .
>
>
>
> Visit our blog: www.cherokee-fire.blogspot.com
>
>
>
>
>
>
>
> NOTICE: The information contained in this email is intended to be solely for 
> the use of the named individual or entity to which it is directed and may 
> contain information that is privileged or otherwise confidential. It is not 
> intended for transmission to, or receipt by, anyone other than the named 
> addressee (or a person authorized to deliver it to the named addressee). It 
> should not be copied or forwarded to any unauthorized persons. If you have 
> received this electronic mail transmission in error, please delete it from 
> your system without copying or forwarding it, and notify the sender of the 
> error by reply email or by calling Cherokee Fire Protection Co. at 
> 888-347-3079 toll free.
>
>
> -----Original Message-----
> From: Thom Mc
> Mahon <[email protected]>
> To: [email protected]; [email protected]
> Sent: Sat, Sep 12, 2009 11:57 am
> Subject: RE: 13D Sauna/Steam Rooms
>
>
>
> This issue came up years ago while working with Jim Bell of Marriott Corp on 
> ne of their assisted living facilities a 13R that I have always used the ame 
> logic since then, and applied it to 13D as well. (1992) At that time arriott 
> had about 2 fires per year in sauna's, typically caused by bottles f body oil 
> or towels placed over the heater. Jim's requirement was to prinkler all 
> sauna's using 300+ degree heads as the emergency cut out for auna controls is 
> typically set in the high 200'F range. We currently nstall 360'F TYCO TY-B 
> either 2.8K or 5.6K depending upon room size. (Yes I now they are STD 
> response, but as we discussed at the time, in a 8x10 room, ny protection is 
> better than none, and Std response Vs. QR will be a matter f only a second or 
> two, with the ambient already over 100'F.) 286'F heads re ok if your 
> emergency cut off is set lower than 236'F, which I've never ound one that 
> low. That's what we do and AHJ's only need to hear this logic nce to accept 
> it.
> Steam rooms, same source at Marriott, "What can burn? Tile walls, floors and 
> eiling, in a basic "Mist" system." Now Marriott used steel studs verywhere, 
> so if your steam room is framed with wood and you have the steam enerator in 
> the typical under bench location, what we've done is put a head n that space, 
> again high temp. If the people or wet towels "s pontaneously ombust" in a 
> steam room not much a sprinkler can do to save them.
> I'd like to hear what others are thinking. 200'F heads will go off way too 
> ften, 286'F may never go off if the emergency cut out is never needed, but  
> know that if a 360'F head goes off, it's either a fire or mechanical amage.
>
> Thom McMahon, SET
> iretech, Inc.
> 560 Copper Ridge Dr
> .O. Box 882136
> teamboat Springs, CO 80488
> el:  970-879-7952
> ax: 970-879-7926
>
> ----Original Message-----
> rom: [email protected]
> mailto:[email protected]] On Behalf Of Bob Knight
> ent: Friday, September 11, 2009 4:33 PM
> o: [email protected]
> ubject: 13D Sauna/Steam Rooms
> I am working on a 13D that has a sauna and steam room.  What temp sprinklers
> hould I use, and is it permissible to use QR instead of Residential?   I'm
> hinking that I will need high temp heads and residentials only go up to 75F, 
> at least the ones that I'm familiar with.
> Thanks,
> Bob Knight, CET
> 660 Hill Rd
> elba, Idaho 83641
> 208) 318-3057
> 208) 495-2057 fax
> [email protected]
> ww.firebyknight.com
> -------------- next part --------------
> No virus found in this outgoing message.
> hecked by AVG - www.avg.com
> ersion: 8.5.409 / Virus Database: 270.13.91/2363 - Release Date: 09/11/09 
> 9:15:00 _______________________________________________
> prinklerforum mailing list
> [email protected]
> ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected] To 
> Unsubscribe, send an email to:[email protected]
> P
> ut the word unsubscribe in the subject field) 
> _______________________________________________
> prinklerforum mailing list
> [email protected]
> ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected] To 
> Unsubscribe, send an email to:[email protected]
> Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to