Again it say's "no less than 30'C above" that does not create a 286'F maximum. 
360 is not less than 30'C above 500'F is not less than 30'C above. Would I 
recommend installing a 2000'F head in a sauna? NO! but small changes in temp 
(less than 100'F) won't delay operation in a confined small room for very long.

To quote Roland "Words have meaning"

Thanks for your input, but we've beat this horse to death.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Forest Wilson
Sent: Saturday, September 12, 2009 12:18 PM
To: [email protected]
Subject: Re: 13D Sauna/Steam Rooms

I wrote the 286 F maximum per the European standard, which says as close to 
highest operating temp rating of unit, but no less than 30* C above highest 
operating temp. So, 286 would be the closest to meet that criteria. I mention 
the Europe standard because although it has no legal standing, the original 
post was for using heads that were standard response anyway. 


Forest Wilson