I think we're mixing terms again. The window sprinkler is a "Specific
application sprinkler" installed in accordance with its listing only!!(Can't
be used for openings, or escalators or mall atriums, unless these are fixed
glass with mullions Horz. and vert. and spacing as per the listing.)

A water curtain NFPA 13 2007 11.3.3.1 to 11.3.3.4 is a series of closely
spaced sprinkler's  with specific uses as defined in chapter 8.(Specifically
8.15.4.1 to 8.15.4.3 and 8.15.16.2, these are the only uses of water
curtains allowed by 13)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Tuesday, September 22, 2009 3:29 PM
To: [email protected]
Subject: RE: Water curtains for windows

No, you're correct.   A REALLY important aspect of using this sprinkler:
it is only listed for fixed glazing.

Steve Leyton
Protection Design & Consulting
San Diego, CA