UFC 3-600-10N, 2-3.1.1.1.   We have been required to use 15 PSI for RP
types, detecting or non-detecting.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark
Sornsin
Sent: Thursday, September 24, 2009 7:12 AM
To: '[email protected]'
Subject: RE: Inadequte Water

Steve:

Which UFL standard is requiring the 12 psi drop across the backflow?
This is the second time I've heard of this but have not yet had to deal
with it (I don't know why not).

I would LOVE to have a sit-down with the 'powers that be' responsible
for the UFC standards. E.g. where do they get the 3,000 sq.ft design
area crap?  They say it's common HPR requirements in the civilian world
- except I worked for FM and we NEVER required 3,000 sq.ft. design areas
for light or ordinary hazard-equivalent occupancies. Maybe they just
want to cover themselves in case a combustible concealed space
appears...

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104-7079

Direct:    701. 280.8591
Fax:        701.280.8739
Cell:        701.371.5759

[email protected]
www.ulteig.com

Confidentiality Notice
This message may contain privileged and confidential information. If you
think, for any reason, this message may have been addressed to you in
error, you   must not disseminate copy or take any action in reliance on
it, and we would ask you to notify me immediately by return email to
[email protected].



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Kowkabany
Sent: Thursday, September 24, 2009 7:18 AM
To: [email protected]
Subject: RE: Inadequte Water

I have the single most frustrating water issue I have ever had going on
right now Greg.  I am working on this small commercial entrance facility
at
a military base in Georgia.  We are only sprinklering a small 3,800 sqft
cargo transfer building and getting the water from the local utility
rather
than the base.

We designed based on modeling data that was the only thing available at
design (there was no water within a mile then) and had no problem making
the
small light hazard wet system work.

Last week the underground was finally finished and we had our main run
up to
the building and some nearby hydrants to test, so we tested them - 55/25
at
750 gpm.  Bad water but still enough to make an little light hazard wet
system work right?

Not once you take a 3,000 sqft design area, a 500 gpm hose allowance due
to
the presence of 300 sqft of OH1 rooms, and a mandatory 12 psi pressure
across the BFP regardless of the fact that it is actually a double-check
-
all mandatory per UFC codes.  After all that, you need 850 gpm at 40 psi
to
make this system work and we are looking at a pump and a tank!

It's a very frustrating situation, so feel free to tell your AHJ he is
not
alone.


Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
616 Davis Street
Neptune Beach, FL 32266
904-652-4200 Phone
904-212-0868 Fax

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4454 (20090924) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4454 (20090924) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to