Isn't an issue of 5 psi really a non issue? I mean, you generally have an AHJ 
mandated safety factor (or should) of 5-10%, a hose allowance that may or may 
not be used, plus calculations that are based upon Hazen-Williams which in 
itself is not as accurate as other methods and provides an additional safety 
margin. 
Not only that but there are usually design options as well. Perhaps the remote 
area could be re-evaluated - maybe there's that head in the closet that really 
doesn't need to be included in the calcs, maybe looping a few of the 
branchlines in the most demanding area would solve things, changing BFP to a 
more friendly friction loss model, did the hydraulics program use the modified 
equivalent lengths based upon NFPA #13 or were these considerably rounded up by 
default (I've seen that)? Could changing sprinklers to larger / smaller orifice 
help, sliding up and down the design density curve to meet actual calculated 
sq. ft'g (if no reductions are taken) etc..
Even without consideration of the above it would seem that 5 psi is not lawsuit 
material - at least to me. As long as this is not storage or extra hazard I 
don't see what the big deal is.
-Ralphy




      