If you look the 3000 s.f. only applies to the hydraulic or room design method. 
It does not apply to the residential or special design.


Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [email protected]
Web Site: http://www.burtellfire.com
 please don't print this e-mail unless you really need to



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Russell
Sent: Wednesday, September 30, 2009 12:59 PM
To: AFSA
Subject: Hotel/Motel and concealed combustible spaces

I'm confronted with a situation that in all my years have never ran across.
It's a 6 story motel/hotel that has combustible concealed spaces which meet
the requirements for the omission of sprinklers but will require the design
area to be a minimum of 3000 sq. ft.. I'm wanting to use the "Dwelling"
design for the quest rooms from NFPA13 but am not sure if this method will
be null and void because of the 3000 sq. ft. requirement. I am aware that
the 'Room Design" method will be wiped out but can find no mention for the
"Dwelling " design method. Can anyone offer advice?

 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to