Without my usual long windedness I agree with Chris. Twenty years of
positive performance, even if a non-intended experiment, proves the
wisdom of retaining the current rule. There is no data to suggest a
change is needed. Committees are acting like Congress: since we've
taken the trouble to meet we'd better meddle with something.

On Wed, Sep 30, 2009 at 1:59 PM, Chris Cahill <[email protected]> wrote:
> Fair point, but we should be "fixing" mistakes in the next edition.  This
> issue goes back to at least 1991 in my quick glance at older editions.  In
> my mind 20 years makes it the new norm even if it was a mistake originally.
> Perhaps then they could/should have arbitrarily took the 3000 out of the
> code based on 20 years of an unintended experiment.
>
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>
> 763-658-4483
> 763-658-4921 fax
>
> Email: [email protected]
>
> Mail: P.O. Box 69
>        Waverly, MN 55390
>
> Location: 4439 Hwy 12 SW
>              Waverly, MN 55390
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Thom McMahon
> Sent: Wednesday, September 30, 2009 3:45 PM
> To: [email protected]
> Subject: RE: Hotel/Motel and concealed combustible spaces
>
> Actually since I see this as a return to the NFPA 13 of old, where you
> sprinkler everything or pay the area density penalty. The fact that when
> residential sprinklers came into 13, their application was inconsistent with
> other QR or FR sprinklers, by not applying the area density penalties. So as
> you say where is the data to support not increasing the area for residential
> heads, like the rest of 13 requires?
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Chris Cahill
> Sent: Wednesday, September 30, 2009 2:44 PM
> To: [email protected]
> Subject: RE: Hotel/Motel and concealed combustible spaces
>
> Geeh so the committee added a substantial new requirement with no data to
> support the change.  Wow, don't they use no data to reject many good ideas
> that IMHO are common sense.  Really have we had any fires start in these
> spaces?  What was the outcome if there are a couple?  I'd think the NFPA
> committee section might call the NFPA data section and ask the question.
> You'd think we'd hear about sprinklered buildings burning down.  I could
> drift into the new(ish) attic rules but that's a dead and decayed horse.
> Sure as @#$% we're going to price ourselves out of fire sprinklers with
> things like this and the overboard parts of NFPA 25.
>
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>
> 763-658-4483
> 763-658-4921 fax
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to