Actually since I see this as a return to the NFPA 13 of old, where you
sprinkler everything or pay the area density penalty. The fact that when
residential sprinklers came into 13, their application was inconsistent with
other QR or FR sprinklers, by not applying the area density penalties. So as
you say where is the data to support not increasing the area for residential
heads, like the rest of 13 requires? 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Wednesday, September 30, 2009 2:44 PM
To: [email protected]
Subject: RE: Hotel/Motel and concealed combustible spaces

Geeh so the committee added a substantial new requirement with no data to
support the change.  Wow, don't they use no data to reject many good ideas
that IMHO are common sense.  Really have we had any fires start in these
spaces?  What was the outcome if there are a couple?  I'd think the NFPA
committee section might call the NFPA data section and ask the question.
You'd think we'd hear about sprinklered buildings burning down.  I could
drift into the new(ish) attic rules but that's a dead and decayed horse.
Sure as @#$% we're going to price ourselves out of fire sprinklers with
things like this and the overboard parts of NFPA 25. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to