"11.2.3.1.8 Restrictions. Regardless of which of the two methods is used, the following restrictions shall apply" Well the residential design found in 11.2.3.5 is not area/density or room design, so per the 2002 and the way I read it, the 3000 sf does not apply.
Joe Burtell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom McMahon Sent: Wednesday, September 30, 2009 1:18 PM To: [email protected] Subject: RE: Hotel/Motel and concealed combustible spaces I believe that this came up in ROP for 2010 and if I'm remembering right the committee said that the 3000 DID apply to the 4 head residential area. Roland are you there? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Joe Burtell Sent: Wednesday, September 30, 2009 1:04 PM To: [email protected] Subject: RE: Hotel/Motel and concealed combustible spaces If you look the 3000 s.f. only applies to the hydraulic or room design method. It does not apply to the residential or special design. Best regards, Joe Burtell, SET, CFPS Burtell Fire Protection Phone: 406.652.7697 Fax: 406.652.7743 Cell: 406.861.4507 Email: [email protected] Web Site: http://www.burtellfire.com P please don't print this e-mail unless you really need to -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Russell Sent: Wednesday, September 30, 2009 12:59 PM To: AFSA Subject: Hotel/Motel and concealed combustible spaces I'm confronted with a situation that in all my years have never ran across. It's a 6 story motel/hotel that has combustible concealed spaces which meet the requirements for the omission of sprinklers but will require the design area to be a minimum of 3000 sq. ft.. I'm wanting to use the "Dwelling" design for the quest rooms from NFPA13 but am not sure if this method will be null and void because of the 3000 sq. ft. requirement. I am aware that the 'Room Design" method will be wiped out but can find no mention for the "Dwelling " design method. Can anyone offer advice? Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)