NFPA 13 (2010) section 11.3.1.2. Looks like according to that the 
3000 sqft applies, unless the concealed space meets the requirements 
for omitting sprinklers.



At 03:17 PM 9/30/2009, you wrote:
>I believe that this came up in ROP for 2010 and if I'm remembering 
>right the committee said that the 3000 DID apply to the 4 head 
>residential area.
>
>Roland are you there?
>
>Thom McMahon, SET
>Firetech, Inc.
>2560 Copper Ridge Dr
>P.O. Box 882136
>Steamboat Springs, CO 80488
>Tel:  970-879-7952
>Fax: 970-879-7926
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Joe Burtell
>Sent: Wednesday, September 30, 2009 1:04 PM
>To: [email protected]
>Subject: RE: Hotel/Motel and concealed combustible spaces
>
>If you look the 3000 s.f. only applies to the hydraulic or room 
>design method. It does not apply to the residential or special design.
>
>
>Best regards,
>
>Joe Burtell, SET, CFPS
>Burtell Fire Protection
>Phone: 406.652.7697
>Fax: 406.652.7743
>Cell: 406.861.4507
>Email: [email protected]
>Web Site: http://www.burtellfire.com
>P please don't print this e-mail unless you really need to
>
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Russell
>Sent: Wednesday, September 30, 2009 12:59 PM
>To: AFSA
>Subject: Hotel/Motel and concealed combustible spaces
>
>I'm confronted with a situation that in all my years have never ran across.
>It's a 6 story motel/hotel that has combustible concealed spaces 
>which meet the requirements for the omission of sprinklers but will 
>require the design area to be a minimum of 3000 sq. ft.. I'm wanting 
>to use the "Dwelling"
>design for the quest rooms from NFPA13 but am not sure if this 
>method will be null and void because of the 3000 sq. ft. 
>requirement. I am aware that the 'Room Design" method will be wiped 
>out but can find no mention for the "Dwelling " design method. Can 
>anyone offer advice?
>
>
>
>Russell Rewis
>
>Brown Automatic Sprinklers, Inc.
>
>107C Hemlock Street
>
>Valdosta, Georgia 31601
>
>229-244-8130
>
>[email protected]
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to