Thom,

Well, I'm not Roland, but I remember a discussion with him where this 
came up, and at that time he directed me to the ROP, and what'll be 
included in the 2010 edition.

Here it is:
13-322a Log #CP313 AUT-SSD Final Action: Accept
(11.3.1.2, A.11.3.1.2 (New) )
Submitter: Technical Committee on Sprinkler System Discharge Criteria,
Recommendation: Add new text to read as follows:

11.3.1.2* Unless the requirements of 11.2.3.1.4(4) are met for buildings 
having unsprinklered combustible concealed spaces, as described in 
8.15.1.2 and 8.15.6, the minimum design area of sprinkler operation for 
that portion of the building shall be 3000 ft2 (279 m2).

11.3.1.2.1 The design area of 3000 ft2 (279 m2) shall be applied only to 
the portion of the residential sprinklers that are adjacent to the 
qualifying combustible concealed space.

A.11.3.1.2 It should be noted that the provisions of Section 11.2 do not 
normally apply to the residential sprinkler design approach. The 
reference to 11.2.3.1.4(4) is merely to provide a consistent approach 
between the occupancy hazard fire control approach and the residential 
sprinkler design approach with respect to unsprinklered combustible 
concealed spaces Renumber remaining sections accordingly.

Substantiation: After further consideration the committee now believes 
that the requirements for the 3000 sqft. design area that are presently 
being applied to quick response sprinklers are appropriate for 
residential sprinklers as well.
Committee Meeting Action: Accept
Number Eligible to Vote: 28
Ballot Results: Affirmative: 23 Negative: 2
Ballot Not Returned: 3 Blumenthal, M., Madrzykowski, D., Smith, P.

And in the new edition of the standard, that text is present, as well as 
the annex note.
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website





Thom McMahon wrote:
> I believe that this came up in ROP for 2010 and if I'm remembering right the 
> committee said that the 3000 DID apply to the 4 head residential area.
>
> Roland are you there?
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Joe Burtell
> Sent: Wednesday, September 30, 2009 1:04 PM
> To: [email protected]
> Subject: RE: Hotel/Motel and concealed combustible spaces
>
> If you look the 3000 s.f. only applies to the hydraulic or room design 
> method. It does not apply to the residential or special design.
>
>
> Best regards,
>
> Joe Burtell, SET, CFPS
> Burtell Fire Protection
> Phone: 406.652.7697
> Fax: 406.652.7743
> Cell: 406.861.4507
> Email: [email protected]
> Web Site: http://www.burtellfire.com
> P please don't print this e-mail unless you really need to
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Russell
> Sent: Wednesday, September 30, 2009 12:59 PM
> To: AFSA
> Subject: Hotel/Motel and concealed combustible spaces
>
> I'm confronted with a situation that in all my years have never ran across.
> It's a 6 story motel/hotel that has combustible concealed spaces which meet 
> the requirements for the omission of sprinklers but will require the design 
> area to be a minimum of 3000 sq. ft.. I'm wanting to use the "Dwelling"
> design for the quest rooms from NFPA13 but am not sure if this method will be 
> null and void because of the 3000 sq. ft. requirement. I am aware that the 
> 'Room Design" method will be wiped out but can find no mention for the 
> "Dwelling " design method. Can anyone offer advice?
>
>  
>
> Russell Rewis
>
> Brown Automatic Sprinklers, Inc.
>
> 107C Hemlock Street
>
> Valdosta, Georgia 31601
>
> 229-244-8130
>
> [email protected]
>
>  
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to