So to avoid the 3,000 SF application we need to include 4 hour horizontal
separations very 4-floors so we can still apply 13R where the onerous large
MRA isn't included?  Naturally I'm assuming the sprinklers under the
balconies will control vertical exterior fire spread.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, October 01, 2009 11:18 AM
To: [email protected]
Subject: Re: Hotel/Motel and concealed combustible spaces

To answer the primary question, as confirmed in the 2007 Sprinkler  
Handbook (page 507), the 3000 sf remote area is CURRENTLY applicable  
only to the occupancy hazard approach and NOT to the residential  
design approach.  As pointed out, that will no longer be the case  
starting with the 2010 edition.

I agree with most of what everyone has said but just because the  
residential sprinkler was originally incorporated into 13 in a very  
sloppy fashion is no reason NOT to remedy it.  For instance, the  
original fire testing for the listing of residential sprinklers lasted  
10 minutes (even if the fire growth was increasing at the end, it was  
a pass).  Now 10 minutes is fine for 13D but a high rise condo should  
have a tad more assurance of successful control.  That's why we treat  
them as a hybrid device and calc at the most demanding based on their  
either listing discharge or the 0.1 using SxL.

Bottom line is that it is what it is.

Roland

On Sep 30, 2009, at 11:59 AM, Russell wrote:

> I'm confronted with a situation that in all my years have never ran  
> across.
> It's a 6 story motel/hotel that has combustible concealed spaces  
> which meet
> the requirements for the omission of sprinklers but will require the  
> design
> area to be a minimum of 3000 sq. ft.. I'm wanting to use the  
> "Dwelling"
> design for the quest rooms from NFPA13 but am not sure if this  
> method will
> be null and void because of the 3000 sq. ft. requirement. I am aware  
> that
> the 'Room Design" method will be wiped out but can find no mention  
> for the
> "Dwelling " design method. Can anyone offer advice?
>
>
>
> Russell Rewis

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to