Semantics perhaps 20 years doesn't make it right it makes it the norm.
There are a lot of normal things in this world that ain't right.  It makes
it the standard to work from.  

As far as storage densities that goes back even further and I do agree with
you on the shaky creation.  But I ask are they wrong?  Do we have failure
when systems are installed correctly with the code density matching the
hazard?  I don't think so.  So right or wrong the 20 plus year experiment
has been very successful here too.  I'd also suggest these have been tested
many more times than fire in 13 residential designs with a 3000 sq.ft.
design area.  Also bear in mind adding more water below the fire really
doesn't help much.  The 3000 is a dumb requirement IMHO in the first place.


Also subsequent research has shown large orifices at the same density works
better.  The code has made that adjustment.  Manufactures developed a lot of
choices.  Also practical design in these parts at least drives the orifice
size as close to 7 as possible.  We don't have any pressure to waste. Even
cases where a little over flow to get to 7 is worth it.  If you have 100 psi
plus you might save a few bucks a head and go with a smaller orifice than we
would.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Wednesday, September 30, 2009 4:58 PM
To: [email protected]
Subject: RE: Hotel/Motel and concealed combustible spaces

>From the # of ROP's I'd say they aren't looking for something to meddle
with, only responding to a proposal by someone just like us.

As for the 20 years make it right, does anyone really believe that the
storage densities derived from so few tests and then extrapolated are really
the most affordable protection? Or the best?

I don't think that the data is there to support either position as far a
residential 4 head designs go, but I do find it ironic that a 20 story
residential tower is life safety, and a 10 story office tower is control
mode protection. Who's more at risk?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Wednesday, September 30, 2009 3:46 PM
To: [email protected]
Subject: Re: Hotel/Motel and concealed combustible spaces

Without my usual long windedness I agree with Chris. Twenty years of
positive performance, even if a non-intended experiment, proves the wisdom
of retaining the current rule. There is no data to suggest a change is
needed. Committees are acting like Congress: since we've taken the trouble
to meet we'd better meddle with something.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to