Just got off the phone with Tyco. FYI if you can keep a 22" deflector you do not need to look at the special application stuff. So depending on stem oc dimensions you might get to 22-24" deep before you have to go with baffles.
Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Geoff Dyce Sent: Tuesday, October 27, 2009 7:37 AM To: [email protected] Subject: RE: Tyco EC 14 & Double Tee's Just an opinion but EC hds. require the baffles as noted for, I believe, all mfgrs. EC heads in concrete tee construction. If you look at regular QR sprks and not EC, it does not appear that you need baffles. G -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Monday, October 26, 2009 5:05 PM To: [email protected] Subject: Tyco EC 14 & Double Tee's In the Design Criteria these heads are listed for the generic obstructed construction. Great, 1-6" down 22" max etc. But then there is a special application for concrete tee's that gives you up to 31" down if you meet all the other criteria. Think baffles 32' o.c. So the question is if I can hold the 22" and meet the normal obstruction rules can I use these under tee's like normal obstructed construction or do I still have to use the special application requirements? (Tyco is closed for the day) I think the answer is yes. I think the special application is only for an exception to the "exception" that allows 22" down compared to the normal 1-12". But I can read it either way. In this case I'd like to stick with 22" because I can with the particulars on the job. So I have a biased opinion. And I'm only bidding so not in a pinch (yet). Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)