Chris.  Over 32 ft in lgth, with EC heads, you will need baffles.  Says so
in the specs!  It does not say this for 5.6 or 8.0 std or QR sprks.  I
believe the 32-0 lgth is the deciding factor for EC heads.
G

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Tuesday, October 27, 2009 8:51 AM
To: [email protected]
Subject: RE: Tyco EC 14 & Double Tee's

Just got off the phone with Tyco.  FYI if you can keep a 22" deflector you
do not need to look at the special application stuff.  So depending on stem
oc dimensions you might get to 22-24" deep before you have to go with
baffles.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Geoff Dyce
Sent: Tuesday, October 27, 2009 7:37 AM
To: [email protected]
Subject: RE: Tyco EC 14 & Double Tee's

Just an opinion but EC hds. require the baffles as noted for, I believe, all
mfgrs. EC heads in concrete tee construction.  If you look at regular QR
sprks and not EC, it does not appear that you need baffles.
G
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Monday, October 26, 2009 5:05 PM
To: [email protected]
Subject: Tyco EC 14 & Double Tee's

In the Design Criteria these heads are listed for the generic obstructed
construction.  Great, 1-6" down 22" max etc.  But then there is a special
application for concrete tee's that gives you up to 31" down if you meet all
the other criteria.  Think baffles 32' o.c. 

 

So the question is if I can hold the 22"  and meet the normal obstruction
rules can I use these under tee's like normal obstructed construction or do
I still have to use the special application requirements?  (Tyco is closed
for the day)

 

I think the answer is yes.  I think the special application is only for an
exception to the "exception" that allows 22" down compared to the normal
1-12".  But I can read it either way.  In this case I'd like to stick with
22" because I can with the particulars on the job.  So I have a biased
opinion. 

 

And I'm only bidding so not in a pinch (yet).        

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to